    on a universal motor (condenser motor)
    it can be used for 1/6 up to 1/3 hp by changing speeds..
    and caps the motors are rated at 1075 rpm with 2 speeds
    if lower speed is used for 1/6 hp does it drop the rpms
    or just amps

    i should know this but i don't so go easy on me!!

  2. #2
    Join Date
    Feb 2005
    Location
    Dothan, Al
    Posts
    3,461
    Post Likes
    Horsepower has nothing to do with speed. 1/6th will pull less current and drive smaller devices than a 1/3rd, but the speed will be essentially the same.
    Speed on ac motor is dependent upon no.of poles, and freq.

  3. #3
    Join Date
    Jul 2005
    Posts
    6
    Post Likes
    bornriding is right on a condenser,horsepower tells you how big of a blade it can pull, and rpm's tell you how fast it is going to go.

  4. #4
    Join Date
    Jul 2004
    Location
    Southern Alabama
    Posts
    448
    Post Likes
    I don't necessarily agree with you guys.

    Yes the speed on a motor is mainly controlled by the formula: RPM =(120*60)/#poles. Where the 60 is the line freq of 60 hz.

    So, a 2 pole motor basically runs at 3600 RPM. But then there's slip. Slip is the diference between armature speed and the electrical field rotation speed (or synchronous speed). For a motor to have any torque there will always be armature speed<synchronous. Synchronous motors are the exception, but are designed to operate at synchronous. The more load, the more slip a motor will have.

    Now, those multi-hp motors are not changing the number of poles. The speed taps are taps on different places of the armature coil; a form of field weakening. This reduces the effective hp the motor can provide. So what you basically have a controlled slip motor to get the RPM you want. The motor must have the correct load to get the desired RPM. Unload this motor and the RPM will be the same for all the taps; which is not the same for a true multi-pole motor.

  5. #5
    Join Date
    Jul 2005
    Location
    north carolina
    Posts
    20
    Post Likes
    Thread Starter
    ok i think i have it...
    so changing the speed taps on a multi hp motor only changes hp and not rpm....

    i understand all about the rpm and hp was just unsure about if the rpms were changed by the speed taps when the hp was changed....

    so that being the case then why on a blower motor when speed taps are changed you get either a low speed med and high speed difference and doesn't it change rpms when speeds are changed...

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    The rpm will change on those motors.

    We switched tho them about 6 monthes ago.

    Follow the instructions with them for the hp, and rpm you need.

  7. #7
    Join Date
    Jul 2005
    Location
    north carolina
    Posts
    20
    Post Likes
    Thread Starter
    i've read the little book that comes with them but all it tells me is about hp not rpms
    we use the first call motors from lennox

    thanks i will try to fine more info from lennox

  8. #8
    igwt777 is offline Professional Member - T&B bad email address
    Join Date
    Jul 2005
    Posts
    172
    Post Likes
    Originally posted by stkepo
    ok i think i have it...
    so changing the speed taps on a multi hp motor only changes hp and not rpm....

    i understand all about the rpm and hp was just unsure about if the rpms were changed by the speed taps when the hp was changed....

    so that being the case then why on a blower motor when speed taps are changed you get either a low speed med and high speed difference and doesn't it change rpms when speeds are changed...
    HP=Torqe RPM=speed

    So if you increase or decrease HP it won't affect the motor RPM's.

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    The ones we use are ao smith. Sourse one.
    You can change the hp, or rpm, or both.

  10. #10
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Originally posted by beenthere
    You can change the hp, or rpm, or both.
    Actually, all you can only lower is the HP, the free RPM stays the same. "Free RPM" is the rpm with no load on the shaft.

    The only way to lower the free RPM is to change the number of poles, change the voltage, or change the frequency.

    Some of the motors I have seen allow you to fine tune the operation of the motor a little by changing run capacitors.

    Lowering the HP, but keeping the same load, will lower the speed due to increased slip.

    The HP taps on these universal condensor fan motors are essentially the same thing as the "speed" taps on a multispeed blower motor, wich actually only change the HP of the blower motor.
    Completely unloaded with no load on the shaft, the motor will spin at the same speed, regardless of wich tap is used, same with a blower motor.
    With the same load on the motor, the RPM will be higher with the hither power taps and lower with the lower power taps.

    I personally don't use these motors, exept when given one by the OEM as a replacement.

    I keep roughly 20 different direct drive blower and condensor fan motors on my truck, about 24 total, and I go get an OEM motor if one on my truck isn't a nearly identacle match. Fortunatly just about every OEM has parts distribution within about a 15-20 minute drive of nearly my entire service area.

    If you insist on using the muliti HP universal motors, note that they come in 1075 and 825 RPM varieties, and in different ranges of HP. They also have more than one height of motor and choices of sleeve or ball bearings.
    Generally it is not good to use the motor that goes up to 1/2 hp to replace a 1/5 hp motor, even though the motor is rated to do so. Using the lower HP taps on them will result in a motor that runs a bit hot, and shortens the potential lifespam of the motor.
    In order for these multi HP "universal" motors to be worth stocking, you need to stock 6 different part numbers on your truck.

    It will always, 100% of the time, be better to use a motor with the same speed, horspower and electrical ratings as the motor you are replacing.

    [Edited by mark beiser on 07-20-2005 at 01:45 AM]

  11. #11
    Join Date
    Jul 2004
    Location
    Southern Alabama
    Posts
    448
    Post Likes
    Here's a link to Fasco. All your questions will be answered once you download the PDF file.

    http://www.fasco.com/fasfacts.asp

  12. #12
    Join Date
    May 2005
    Posts
    64
    Post Likes

    Cool

    tell you guys the truth my service manager ordered a much of those motors and the get u thru a cooling season but they dont seem to last ong i think is beter to keep single horsepower motors on van i know someone will say i can use it for more units but its just what i think

  13. #13
    Join Date
    Jul 2005
    Location
    north carolina
    Posts
    20
    Post Likes
    Thread Starter
    thanks for the link it's a big help......

    thank all for the knowledge
    14 years and i'm still learning
    guess i always will

    thanks again!!!

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •