Results 1 to 9 of 9
  1. #1
    Join Date
    Feb 2008
    Location
    Pensacola Florida
    Posts
    33
    Post Likes

    Turbocor TT300 Bearing Calibration issue

    I have never had this issue before so if anyone has experience with this I would greatly appreciate any suggestions.

    TT300 - trying to prepare for an initial start up. During the initial bearing calibration it goes thru all the steps and then fails at the end during shaft levitation. Calibration Failed (Levitation) is the message displayed.

    Also, the calibration does not sound the same as I am used to hearing the knocking and pinging.

    I have the modbus disconnected. Im in calibration mode. Also i did try this is the latest 3g software and the previous version with the same results.

  2. #2
    Join Date
    Dec 2006
    Location
    Somewhere in Canada
    Posts
    84
    Post Likes

    Calibration and Troubleshooting

    The attached information sheets may be of value to you in the calibration and / or troubleshooting the bearing calibration issue. These sheets are from a largermanual.

  3. #3
    Join Date
    Dec 2006
    Location
    Somewhere in Canada
    Posts
    84
    Post Likes

    Troubleshooting bearing calibration

    Please find this Bearing Calibration Troubleshooting section of interest.

  4. #4
    Join Date
    Oct 2010
    Posts
    344
    Post Likes
    Check earlier t-cor threads,several have stated that they had issues with liq. ref. causing calib. problems,may have to isolate comp. recover gas and then calibrate.

  5. #5
    Join Date
    Apr 2010
    Posts
    61
    Post Likes
    Make sure yor com cable to your micro is unplugged

  6. #6
    Join Date
    Mar 2006
    Posts
    12
    Post Likes
    Yes, liquid slugging causes calibration problems. Evacuate compressor and retry.

  7. #7
    Join Date
    Jul 2011
    Posts
    2
    Post Likes
    use the version 80 software/monitor package. I have had the same issues with 83 and 86 software-went back to 80 and everything went fine. Recently loaded 3g, but haven't used it to calibrate yet, so no experience.

  8. #8
    Join Date
    Feb 2008
    Location
    Pensacola Florida
    Posts
    33
    Post Likes
    Thread Starter
    thanks for reply- actually version 66 and version 80 do work. still unable to get 3g to work but i think its my laptop because it works fine on another one


    Quote Originally Posted by hookjaw24 View Post
    use the version 80 software/monitor package. I have had the same issues with 83 and 86 software-went back to 80 and everything went fine. Recently loaded 3g, but haven't used it to calibrate yet, so no experience.

  9. #9
    Join Date
    Aug 2009
    Location
    Ontario, Canada
    Posts
    64
    Post Likes
    Downlaod the latest version of 3G, I believe they had some issues with the earlier version of 3G, not sure if that was part of it

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.