Results 1 to 9 of 9
-
04-20-2011, 10:07 AM #1
Professional Member
- Join Date
- Feb 2008
- Location
- Milton Florida
- Posts
- 33
Turbocor TT300 Bearing Calibration issue
I have never had this issue before so if anyone has experience with this I would greatly appreciate any suggestions.
TT300 - trying to prepare for an initial start up. During the initial bearing calibration it goes thru all the steps and then fails at the end during shaft levitation. Calibration Failed (Levitation) is the message displayed.
Also, the calibration does not sound the same as I am used to hearing the knocking and pinging.
I have the modbus disconnected. Im in calibration mode. Also i did try this is the latest 3g software and the previous version with the same results.
-
04-21-2011, 06:56 AM #2
Professional Member
- Join Date
- Dec 2006
- Location
- Somewhere in Canada
- Posts
- 80
Calibration and Troubleshooting
The attached information sheets may be of value to you in the calibration and / or troubleshooting the bearing calibration issue. These sheets are from a largermanual.
-
04-21-2011, 07:09 AM #3
Professional Member
- Join Date
- Dec 2006
- Location
- Somewhere in Canada
- Posts
- 80
Troubleshooting bearing calibration
Please find this Bearing Calibration Troubleshooting section of interest.
-
04-23-2011, 05:24 PM #4
Professional Member
- Join Date
- Oct 2010
- Posts
- 101
Check earlier t-cor threads,several have stated that they had issues with liq. ref. causing calib. problems,may have to isolate comp. recover gas and then calibrate.
-
05-18-2011, 11:32 PM #5
Regular Guest
- Join Date
- Apr 2010
- Posts
- 60
Make sure yor com cable to your micro is unplugged
-
05-19-2011, 03:24 AM #6
Regular Guest
- Join Date
- Mar 2006
- Posts
- 12
Yes, liquid slugging causes calibration problems. Evacuate compressor and retry.
-
07-30-2011, 05:41 AM #7
New Guest
- Join Date
- Jul 2011
- Posts
- 2
use the version 80 software/monitor package. I have had the same issues with 83 and 86 software-went back to 80 and everything went fine. Recently loaded 3g, but haven't used it to calibrate yet, so no experience.
-
07-30-2011, 08:29 AM #8
Professional Member
- Join Date
- Feb 2008
- Location
- Milton Florida
- Posts
- 33
-
07-30-2011, 09:55 AM #9
Professional Member
- Join Date
- Aug 2009
- Location
- Ontario, Canada
- Posts
- 48
Downlaod the latest version of 3G, I believe they had some issues with the earlier version of 3G, not sure if that was part of it


Reply With Quote