Results 1 to 10 of 10
    Toledo, Ohio
    Replaced an old Chrysler Air Temp system, I believe the model # was CH 1265, could someone possbly tell me what size the old one was.
    Replaced it with a Rheem 3.5
    No Heat No Cool You need Action Fast
    Tyler TX
    I got a simular one to replace, how do you decifer there model numbers
    HVAC Contractor, Tyler Texas.
    Hi Terry, the 5 would indicate a 5 ton. Not sure what the code is beyond that. Those that start 126X were 6-7 SEER and they had a line in 1977 anyway that were 129X and 7-8 SEER.
    Toledo, Ohio
    Thanks that is what I thought. The customer still had the original installation manual it started at 1261, 1262, 1263,
    1264, and 1265. I couldn't figure out what the 1261 was, I thought 1262 2 ton,,1263 3 ton....etc, but couldn't figure out what the 1261 was, so it confused me a little. No number on the compressor.
    Again Thanks
    Terry
    Where the H have you been?
    Toledo, Ohio
    real busy, thanks for missing me
    Hell you missed all the FUN!
    The 1 was a 1.5 ton.
    Toledo, Ohio
    again thanks for the help.....
    Oddly the Carrier blue book shows a 1265-00 as 45,000 btus,1968 to 1970,and a 1265-02,46 and 47000,1971 and 1972.Then a 1265-03,46,47,45,and 45,1973 thru1977.
    Then in 1978,a 12650cq or cr as 56,000.
    So depending on suffix,could be any of the above,if the book is correct.