    What would lead anyone to think that there is a restriction in this system ???

    Would a retsriction lead to 46 degree SLT ?

  2. #15
    Join Date
    Sep 2002
    Posts
    511
    Post Likes
    Bornriding, started with 27°subcooling,removed charge and still have 25°subcooling.

    Refrigerant is stacking in the condenser, while removing the refrigerant dropped the suction pressure resulting in a lower SLT.

    I think that there may be a restriction across the liquid line drier or the TXV is not metering,(check the position of the Bulb on the Suction line.)


  3. #16
    Join Date
    Sep 2002
    Posts
    511
    Post Likes
    The more I thought about it....it couldn't be a restriction or the superheat would be alot higher.

  4. #17
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    The reason its stacked in the condenser is because there is no load. Born is right, there is no restriction if the information we got is correct.

  5. #18
    Join Date
    Mar 2002
    Location
    Richmond, Virginia
    Posts
    4,264
    Post Likes
    Measure CFM. Check duct static pressures. Sounds like insufficient air across evaporator coil. Make sure blower wheel is clean and dampers/registers are open.
    There is nothing more frightful than ignorance in action....Mark Twain