07-18-2005, 10:11 PM #1
Last call today on 2 story medical building with 2nd story reaching 80 degrees controlled by Trane Voyager, Trane Zone sensors (7), Trane Varitrac.
Voyager is 10 ton, 2 compressors, heat pumps & electric back up but one compressor running. All zones calling for cooling, by-passed closed, most zones 5 to 8 degrees above set point yet Varitrac screen shows calling for one compressor only, the other not energized. OA sensor correct, discharge air sensor correct, all zone sensors correct, discharge air set point is 55 degrees but has correct reading of 67 degrees discharge in unit.
Varitrac should have 2nd stage energized. Can't shut system down because I would run all the patients out due to heat build up.
But the Varitrac is not indexing 2nd stage to come on.
And quick thoughts?"The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
- Alexis de Toqueville, 1835
-
07-19-2005, 07:48 AM #2
Delta
Check to see if veritrac is set up for 2 heat 2 cool or look at how many compressors the veritrac states that it has, it sounds like it thinks it has only 1 compressor ???
-
07-19-2005, 02:17 PM #3
jtricor
Thanks. I only had time to check the view and status menus and since the status menu listed two compressors with #1 on and #2 off I assumed it was set up for two compressors. But that assumption could be wrong. If so, it's probably been this way since installation 3 years ago.
Problem is I ran out of time as the building was closing up and they wanted me out. Amazing that customers will beg you to get there and then won't hang around to give us time to finish what we started.
I hope to get back there in the next couple of days."The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
- Alexis de Toqueville, 1835
-
07-19-2005, 05:02 PM #4
I have seen this happen alot, for the most part the veritrac will take off and run system with out any set-up so alot get left like that, just about all that I have looked at are still running in the factory default set-point I have even seen a jumper so that both compressors come on if there is a call for cooling because they didnt have a way to set the varitrac up.
-
07-19-2005, 05:36 PM #5
Professional Member - T&B bad email address
- Join Date
- Jul 2005
- Posts
- 172
That is a "nice temporary fix" a Friday at 5:00PM. I've seen tha same on 2 stage cooling thermostats a jumper cable from y1 to y2. Next thing is that you have to fix it correctly because you are the next one there. Why are so many people that don't mind to do things the way they should be done!!!Originally posted by jtricor
I have seen this happen alot, for the most part the veritrac will take off and run system with out any set-up so alot get left like that, just about all that I have looked at are still running in the factory default set-point I have even seen a jumper so that both compressors come on if there is a call for cooling because they didnt have a way to set the varitrac up.
-
07-19-2005, 09:05 PM #6
Regular Guest
- Join Date
- Jan 2004
- Posts
- 389
Well, it would be great if you had the Tracker software and a laptop, but you can go thru the menues. I would first run the unit thru test mode in make sure everything stages on. Then I would review all menues for any mis configs, you most likely will find a mis-config or setup erro.Good luck.
-
07-19-2005, 09:31 PM #7
bku
you do not need any real software to talk to a veritrac or a tracker just use term mode with a cable that I have stated (with a part #) been using this for more than 10 years diffrent cable on the old command units I would be willing to e-mail anyone this so called software
-
07-19-2005, 11:57 PM #8
jtricor
You guys with your laptops will choke on this, yes, I also have a laptop, but I have never connected to any automation systems with a laptop. I run the system doing the hardware- software method....I set it up by the switches, buttons, menus, whatever.
Maybe being able to dial in would be nice but I see no reason to continue to chase down the many versions of software put out by all the different manufacturers.
But, jtricor, if you have something that would make my life easier in setting Varitracs up I would appreciate the Email. My Email is on my profile.
Years ago Johnson was setting up a ton of Data Aires that I was doing start & tests on. Three of them they could not set up through their phone modem so they called me on the job and begged me to manually set them up so they would not have to make a 90 mile trip. I'll stick with hands on setups unless I can find a source of quick, inexpensive, dependable software for most of the units I work on. So far I have not."The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
- Alexis de Toqueville, 1835
-
07-20-2005, 12:48 AM #9
Professional Member
- Join Date
- Jul 2000
- Location
- Dallas,Texas
- Posts
- 4,819
I too, would be interested in the email you are offering.
My email is in my profile.
-
07-20-2005, 02:38 PM #10
I will do that with some more info for the two of you
-
07-20-2005, 07:56 PM #11
Professional Member
- Join Date
- Oct 2003
- Location
- Michigan
- Posts
- 666
If you have the "older" Tracker or CCP all you need is Hyper terminal, if this is a recent install you will need Tracker software......new CCP ships with the needed software unless that changed recently.Originally posted by jtricor
bku
you do not need any real software to talk to a veritrac or a tracker just use term mode with a cable that I have stated (with a part #) been using this for more than 10 years diffrent cable on the old command units I would be willing to e-mail anyone this so called software
-
07-20-2005, 08:44 PM #12
Regular Guest
- Join Date
- Jan 2004
- Posts
- 389
JTRICOR
Can you spell Varitrac? daaa I know you can use old hyper term, but the guy has no laptop, daaaa maybe you can send him yours.
-
07-20-2005, 08:45 PM #13
I have had similar troubles with the Voyager controls. After doing a bunch of troubleshooting, I was assisting another tech over the radio, the problem turned out to be a failure in the economizer control module attached to the damper actuator. I had him disconnect the harness plug and the unit began operating as it should. In fact, when in test mode it would only bring up to the 1st stage of cooling and go no farther.
He disconnected the plug and it would "test" through every mode and came up with both stages of cooling as demended after the unit was reset.
My Voyager "black book" makes note of erratic unit operation as most likely originating with a failure in the econmizer module.
Maybe this will help.Two things are infinite: the universe and human stupidity; and Im not sure about the universe. Albert Einstein