Results 1 to 6 of 6
  1. #1
    Join Date
    Jul 2005
    Posts
    2
    Post Likes
    Using a HVAC software program I calculated the heat gain for my house to be approximately 32000 BTUs. However, the software for some reason won't let me change the outdoor summer design condition. It defaults to 105 degrees and I think for my area the recommendation is 91 degrees. I'd like to add a little buffer to the program of 7 degrees. My question is, approximately how much would the heat gain change from 32000 BTUs at 105 degrees to 98 degrees. Would it be enough for me to want to go with a 2.5 Ton versus a 3 Ton?
    Thanks!

  2. #2
    Join Date
    Apr 2002
    Location
    Omaha, NE
    Posts
    1,561
    Post Likes
    Originally posted by bdschet
    Using a HVAC software program I calculated the heat gain for my house to be approximately 32000 BTUs. However, the software for some reason won't let me change the outdoor summer design condition. It defaults to 105 degrees and I think for my area the recommendation is 91 degrees. I'd like to add a little buffer to the program of 7 degrees. My question is, approximately how much would the heat gain change from 32000 BTUs at 105 degrees to 98 degrees. Would it be enough for me to want to go with a 2.5 Ton versus a 3 Ton?
    Thanks!
    Where are you located? Maybe the summer design temp. IS 105F.
    If I knew your approx. location I can look in The Manual J. As to how much more gain at 105, that depends on the total square footage of the house that is exposed to outside temps.

  3. #3
    Join Date
    Apr 2002
    Location
    Omaha, NE
    Posts
    1,561
    Post Likes

    GEEZ, it was in your profile

    I guess I should have looked in your profile. It says Baltimore, and yes my Manual J says Baltimore summer design temperature (2.5%) is 89F. -city office and 91F. - airport.

  4. #4
    Join Date
    Sep 2001
    Location
    Vancouver Canada
    Posts
    996
    Post Likes
    pay for the program and that will allow you to change the design temps.
    "Go big or Go Home"

  5. #5
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    8,132
    Post Likes

    Question Equipment Selection

    Originally posted by bdschet
    Using a HVAC software program I calculated the heat gain for my house to be approximately 32,000 BTUs.

    It defaults to 105 degrees and I think for my area the recommendation is 91 degrees. I'd like to add a little buffer to the program of 7 degrees.

    My question is, approximately how much would the heat gain change from 32,000 BTUs at 105 degrees to 98 degrees. Would it be enough for me to want to go with a 2.5 Ton versus a 3 Ton?
    A 3-ton may not provide enough ( 32,000) Sensible Cooling.

    S.H.R. = 0.74 for some equipment mfgs, so 3-ton unit generally provides 36,000 BTUh Total /26,640 BTUh Sensible.

    7'F less for Outside Design (98'F versus 105'F)
    may lower the calculated load by ~4,000 + BTUh
    for the walls and ceilings.

    __ Seems like__ you may need ~3 Ton to
    address YOUR 98'F Design temperature.

    S.H.R. = Sensible Heat Ratio
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  6. #6
    Join Date
    Aug 2003
    Posts
    626
    Post Likes
    There is no need to add a buffer. Manual J is already 25% oversized. The best thing for you to do is check your ducts for leakage (if they are outside the thermal envelope) and seal all holes between the attic and rooms below. This way you are saving winter and summer.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.