    I have an XL14i Trane model 4TTX4048A. I am beginning to suspect the coil is undersized ( freezes in very hot weather ) or is one lacking a TXV/TEV. Unit was bought as a package with a gas furnace. The coil is Trane model RXC05453HPCO. Does anyone know if this coil should be sufficient for the condensing unit under most circumstances? Thanks.

  2. #2
    Join Date
    Jan 2005
    Posts
    340
    Manufacturer: THE TRANE COMPANY

    ARI Reference Number: 246818
    ARI Program: AC
    ARI Type: RCU-A-C

    Trade/Brand Name: XL14i
    NAECA Designation: Yes
    Outdoor Model Number: 4TTX4048A1

    Indoor Unit(s): RXC054S3
    Ventilation Rate:

    Product Performance Ratings
    ARI Rating
    Cooling Capacity (Btuh): 48000

    SEER Rating (Cooling): 13.50

    --------------
    TravisFL Note: Combination could be 14.0 SEER if installed with select furnaces.

    [Edited by travisfl on 07-16-2005 at 02:56 PM]

  3. #3
    Join Date
    Feb 2005
    Location
    Central Alabama
    Posts
    466
    freezing could be caused by low air flow due to dirty coil or dirty filter etc.(under chared) If fixed bore orfice it could very well be oversized orfice allowing liquid back to compressor dropping line temperature below 32 degrees F. Also if equiped with TXV it could be a loose sensing bulb and or many other things

  4. #4
    Join Date
    Feb 2005
    Location
    Central Alabama
    Posts
    466
    Travisfl That is good info did u find it on net and if so would u tell me where.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,803
    Check your air filter first.
    Then call the installing contractor if the filter is not the cause.
    How old is the unit.

    An over sized piston won't cause it to freeze on very hot days.

    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,803
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Feb 2005
    Location
    Central Alabama
    Posts
    466
    your right not on high ambient day sorry for that thought.

  8. #8
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,189
    Originally posted by lactulose
    I have an XL14i Trane model 4TTX4048A. I am beginning to suspect the coil is undersized ( freezes in very hot weather ) or is one lacking a TXV/TEV. Unit was bought as a package with a gas furnace. The coil is Trane model RXC05453HPCO. Does anyone know if this coil should be sufficient for the condensing unit under most circumstances? Thanks.
    Coil has a TEV inside the cabinet from the factory. As posted, it is an ARI match. You need to get a pro on site to evaluate cause for freezing IF filters are clean and your registers are open.

    [Edited by jrbenny on 07-16-2005 at 04:09 PM]

  9. #9
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Originally posted by beenthere
    bama 101.

    http://www.ariprimenet.org/


    Note; That's at 80 indoor air,75 is a different story.

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,803
    Yeah, I just gave him the link for checking what coils are matches.

    Thats what I thought the original question was about, weather the indoor coil was right for the outdoor.

    Weather its a match for his load conditions or not, is another story.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #11
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    I wish I could figure out how to save the reports from Trane's performance data CD in a form that would show up formated correctly in a post.

    The reports generated by the program show the performance of the equipment matchup at 3 different WB and 4 different DB temperatures with 85, 95, 105 and 115 ambient conditions. It also shows the performance at specific design conditions you input.
    If more government is the answer, then it's a really stupid question.

  12. #12
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Originally posted by mark beiser
    I wish I could figure out how to save the reports from Trane's performance data CD in a form that would show up formated correctly in a post.

    The reports generated by the program show the performance of the equipment matchup at 3 different WB and 4 different DB temperatures with 85, 95, 105 and 115 ambient conditions. It also shows the performance at specific design conditions you input.


    Now that's valuable information,wish they all did it that way.

  13. #13
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    Dash, no kidding, I wish every manufacturer did it like that too.
    Since I started taking hard looks at system performance data, I realized that a lot of the lower priced equipment out there isn't cheeper just because of thinner metal and less marketing.
    Also some of the equipment a few people here like to call overpriced, isn't more expensive just because of how much the manufacturers spend on marketing.
    The more expensive manufacturers equipment generally has more R&D behind it, and performs better at conditions other than the standard ARI conditions the SEER ratings are done at. This is very important to me because the design conditions for my area are considderably different from what the ARI test conditions are.
    If more government is the answer, then it's a really stupid question.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event