    One of my tech's was on a call for a rooftop unit last night, actually it was a split system with a TXV,he told me that as soon as he fired up the compressor the head pressure would sky rocket to 450 psig and trip out the hps. I told him to close off the liquid line service valve and try to see if the unit would pump down, but it would not, it would run the head pressure up but not pull the low side down. any help here would be appreciated.

    Keith

  2. #2
    Join Date
    Jun 2001
    Location
    Michigan
    Posts
    11,968
    Service valve stopper broke off stem and is blocking passage of discharge gas. Just seen something almost identical a few weeks ago. Or somehwere before condenser you got a total blockage.

  3. #3
    Join Date
    Apr 2003
    Location
    the Great Pacific Northwest
    Posts
    607
    I saw one like this once, it was so overcharged the condenser was full (yes full) of liquid the system had a plugged screen before the TXV and the tech kept charging it trying to get the suction up until it tripped. Try purging your hoses or dump some liquid from the liquid line service port into a recovery cylinder and see where you are.

    Dow says "Service valve stopper broke off stem and is blocking passage of discharge gas. Just seen something almost identical a few weeks ago. Or somewhere before condenser you got a total blockage. "

    If this is a split I would assume it has a can and wouldn't have a service valve at the compressor, and the access port would be at the liquid line service port, but if it does and the service port is at the compressor discharge you could have a blockage between the compressor discharge and the condenser

  4. #4
    Join Date
    May 2004
    Posts
    475
    Sent out for a 'no cool' on a sandwich van that had same symptoms.
    Thought I had some kind of restriction before condenser somewhere.

    Not even close.

    Another tech was sent to this job the day before but SM didn't hear back from him and figured he ran out of time and never made it.
    Turns out, he did.

    He found system empty, 200# nitrogen, leak check, Nextel goes off...

  5. #5
    Join Date
    May 2001
    Location
    Bennington, Vermont U.S.A.
    Posts
    13,859
    One other thing not mentioned. If it is a split system make sure that there is not a check valve installed in the discharge line. Carrier is good for this. A check valve in the discharge line prevents liquid migration back to the head of the compressor. If this is not working you could get the systoms as posted.

  6. #6
    Join Date
    Jun 2005
    Location
    Chicago IL
    Posts
    3

    high head pressure

    Thanks for the replies, It turned out to be a plugged liquid line filter drier between the final run of the condenser coil and the L.L. service valve, better trust my instincts next time!

  7. #7
    Join Date
    Apr 2003
    Location
    the Great Pacific Northwest
    Posts
    607
    How long and what size of line set did this system have?