Results 1 to 10 of 10
Thread: Static Pressure Again?
07-15-2005, 04:50 PM #1
- Apr 2005
- Sacramento, CA
- 8
I had a 4 ton Carrier Infinity heat pump (2 speed with VS fan coil) installed (attic) two months ago. Just turned on the AC two weeks ago. The system is qreat - cools well, even temperature throughout house, and is quiet (except on high). Checking the system through the stat, I noticed that static pressures were higher than I expected based on general information I have picked up on this site.
882 CFM -- 0.35
1400 CFM --0.97
1600 CFM --1.19
The system typically operates in the 800 to 1400 CFM range and only goes to the highest speed when there is a >2°F difference in actual and demand temperatures. The installer says these readings are normal. Also, the stat called for filter cleaning after only 1 week of operation. I cleaned it even though it looks brand new. After 1 more week it is calling for cleaning again. No faults are reported. Any thoughts?
07-16-2005, 11:27 AM #2
Banned
- Aug 2002
- Office and warehouse in both Crystal River & New Port Richey ,FL
- 18,836
1400 at .97,is too high,little room left as the filter gets dirty to stay below the limits..70 is the max we leave them at ,with a clean filter.1600,will likely be so few times,if set for 350 cfms,that it can be over the limit.
It's likely a simple duct modification to get it down,can you post pictures of the ducts?
What city/state are you in?
07-16-2005, 02:55 PM #3
- Apr 2005
- Sacramento, CA
- 8
Thanks Dash,
Ducts are all flex with a centrally located 20 x 30 return grill (alergy gold electrostatic filter) and a 16"dia duct. There are 6 supply ducts off the plennum: 1-5", 2-6", 1-8", 1-10", and 1-14". The 6" and 8" ducts have dampers. Looks like the size on the return duct is limited by the roof line in the attic.
07-16-2005, 03:08 PM #4
Banned
- Mar 2004
- Gone
- 5,340
Through away the electrostatic, and use a plain old blue fiberglass filter until you can have a media filter installed. The electrostatic is way to restrictive.
Your return flex is undersized and you need to have a contractor correct this.
Your supply looks like it would be ok as long as there are not to many turns etc.
A contractor who understands how to diagnose using a magnehelic meter could determine exactly where and what side your problems are on. Changing the filter will help you greatly just for a start.
07-16-2005, 03:18 PM #5
Put a regular air filter in and see if that doesn't drop your static pressure.
Your return duct is just a bit small also.
07-16-2005, 03:24 PM #6
Banned
- Aug 2002
- 18,836
What "made' said is correct.
Magnehelic,manometer will do,Theyneed to test the static,for the supply and return,then decide which is easier tor reduce,usually it's the supply.
Adding a second return may be all thats needed,and is an opportunity to get a return in the master suite.
Now they likely could just increase the existing return duct and grill,to do the same,so if you want a second reurn,ie in the master,it would be fair that you pay the extra cost for that solution.
If they have no idea ,about static ,your may need to call 800-CARRIER,but please let them try to resolve it first.Talk to the owner or service manager.
07-16-2005, 05:26 PM #7
- Apr 2005
- Sacramento, CA
- 8
Thanks all,
I tried a merv 8 pleated filter that they had left as an alternate and it actualy increased the static pressure from .97 to 1.18 at 1400 CFM. I'll contact the installer again next week.
07-16-2005, 05:34 PM #8
Banned
- Aug 2002
- 18,836
Been theres ,suggestion of a "regular" filter is the best till they correct the ducts.
size and thickness of the merv 8?
07-16-2005, 08:05 PM #9
- Apr 2005
- Sacramento, CA
- 8
The merv 8 filter is a naturalaire 1" thick. I put a cheap fiberglass filter in and the SP dropped to 0.82. Without any filter the reading was 0.71. I guess filters do make a big difference
07-16-2005, 10:26 PM #10
Banned
- Aug 2002
- 18,836
Yes they do spread the word!!!LOL