Thread: Sizing up duct-work
-
07-14-2005, 05:02 PM #1
Professional Member
- Join Date
- Aug 2002
- Posts
- 105
I got a small ranch..AC job..
will be installing the AHU in the attic..
I will be adding a 3 -ton unit..
Was wondering how do I figure the Trunk-line...coming out of the discharge on the AHU
the Ranch is 46' Wide
the house is a little under 1400 sq. ft.
thoughts
talk soon
dismas
-
07-14-2005, 05:13 PM #2
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,260
Drawing + ACCA Manual D
Duct layout guidance can only realistically be developed after a floor plan is provided.
... 3-Ton is ~ 1,200 CFM,
... FOR A STARTer :
... AHU outlet duct should be ~1.5 Sq. Feet
... 12" x 18" hard duct at least 6 feet long
Any branches sizing is guessing.
... 800 CFM = 1.0 Sq. Foot ( 12"*12" or 14" diameter )
... 600 CFM = 0.8 Sq. Foot ( 10"*12" or 12" diameter )
Add up all the dP's for straight runs, fittings, outlets on each flow path to assure you have met ACCA Manual D criteria and AHU fan capability.Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
07-15-2005, 09:22 AM #3
Professional Member
- Join Date
- Aug 2002
- Posts
- 105
Sizing up duct work
Thanks Dan,
If I can get you the ..floor plan...could you help me out
until ..I can afford the HVAC Software...
I do have the Manual D...but, can't claim to be a pro..at it
I will be having the duct work..made up at the sheet metal shop...so I am trying to be close ..
talk soon
Dismas
-
07-15-2005, 09:42 AM #4
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,260
Re: Sizing up duct work
O.K., minimal charge for 1,400 Sq. Feet depending on extent of details needed and permitting documentation required.Originally posted by dismas66
If I can get you the floor plan could you help me out until I can afford the HVAC Software
I will be having the duct work made up at the sheet metal shop so I am trying to be close ..
Send .PDF file to
racingdan11 at comcast dot net
___________ @ ________ . _____
( /\ address per Forum rules)
OR can you snail mail if you have the time.
OR FedEx if your schedule dictates.
I can complete in < 1 day after all info is provided.
You need to be Nearly EXACT on a REALISTIC DUCT and AHU layout depending on space allocation as required by buidling structure.
or write for other arrangements
+ necessary buidling design details.
1. City, State
2. House Orientation
3. AHU Location: Qty. 1
4. Insulation
R-__ wall .. ceilings
__ Batt
or __ Spray Foam
5. Window schedule
__ Mfg: Anderson or other
6. Wall Height:
_ 8 9 feet
_ 10 feet
7. One story
8. Special internal gains, if any,
i.e. A-V or computer roomDesigner Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
07-15-2005, 09:57 AM #5
Professional Member
- Join Date
- Aug 2002
- Posts
- 105
Sizing
Thanks Dan,
you can e-mail me
@ joemonahan@comcast.net
pdf file should work
accobat too
talk soon
DISMAS


Reply With Quote