    a customer call no ac.when i got to the customer house, I found the evaperoter totally iced. defrost the ice. it is a heat pump. I hooked the gage. the low side is only 40 psig, more than 40 supreheating.high side 220 psig, the subcooling is almost 0( Maybe I measureed not accurate). is it undercharge or capilary tube restricted?

    [Edited by comfortable air on 07-12-2005 at 07:39 PM]

  2. #2
    Join Date
    Jun 2003
    Location
    Jacksonville, FL.
    Posts
    4,313
    Post Likes
    Dude, aren't you a tech? Sounds like it's low to me but I don't know what the ambients are. Could be possible the RV isn't fully switching over to cool either.

  3. #3
    Join Date
    Nov 2004
    Posts
    213
    Post Likes
    Thread Starter
    Yes. I am. but it is my first time to servie the heat pump.
    ambiet temperature is more than 90f. I don't think rv is not fully open for cooling. it either open or close. it could not be partly open.

  4. #4
    Join Date
    Aug 2002
    Posts
    545
    Post Likes

    Filter

    Did you check the filter, Indoor coil, return air or make sure the blower motor is running? Might as well try a shot of r22.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,617
    Post Likes

    With no subcooling, and high superheat it sounds like a leak.

    Check for a leak.

    Fix the leak, and recharge it.

    Yes, I omitted acouple steps.

    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    Originally posted by special ed
    Could be possible the RV isn't fully switching over to cool either.
    With a 40 suction?

    OP...

    You are working on a heat pump in cooling mode. Why would this be any different than a straight AC at this point? Use what you know about AC and dont get hung up on the fact its a heat pump.

  7. #7
    Join Date
    Jan 2001
    Posts
    17,411
    Post Likes
    Dump a gallon of refrigerant into the system and see what happens..........

  8. #8
    Join Date
    Nov 2004
    Posts
    213
    Post Likes
    Thread Starter
    thank you everybody. the high pressure don't lookes like undercharge. when i met some 40 psig at low side, the high side usually don't over 200. I am sure it is undercharge. but this time is different. the head pressure is not low.
    the evaperator coil and filte is ok. the air volume is also ok. I dump some of gas inside it to increase the head pressure. I will go back to see how is it going. if it is a leakage, the problem will be repeat soon

    [Edited by comfortable air on 07-13-2005 at 11:07 PM]

  9. #9
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    I'm curious but what exactly is ok air volume. Just so we stay on the same page here.


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.