New liquid line connected to new a-coil in new air=handler.Line never even connected to new condensing unit.A co-worker installed the new inside unit and liquid line 1 week ago and sealed it/charged it with nitrogen.This is on second floor and line ends in basement.Today I cut the end off to finish the line to outside and oil starts dripping out the end.A lot of it.This is new inside system & a-coil and neither ever hooked up to a condensing unit.Anyone ever ran it to this?
-
07-13-2005, 10:52 PM #2
probably pushed oil out of his guages with nitrogen.
-
07-13-2005, 10:53 PM #3
Regular Guest
- Join Date
- Mar 2005
- Posts
- 65
Thanks.Very obvious now.
-
07-13-2005, 10:53 PM #4
It was vac pump oil. If you dont close of the pump when you shut it off it gets sucked into the line.
Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced
-
07-13-2005, 11:02 PM #5
Regular Guest
- Join Date
- Mar 2005
- Posts
- 65
I'm not sure this guy would have pulled a vacuum just to seal the line while not hooking it to a unit, but I'll check.Thanks for that info though.so you close the pumps valve & t hen turn pump off.Thanks.Still new don't you know.