    Can somebody educate me on what a line set trap is for?

  2. #2
    igwt777 is offline Professional Member - T&B bad email address
    Join Date
    Jul 2005
    Posts
    172
    Post Likes
    Refrigerant or condensate???

  3. #3
    Join Date
    Feb 2001
    Posts
    472
    Post Likes
    Thread Starter
    Isn't a line set always for refrigerant?

  4. #4
    igwt777 is offline Professional Member - T&B bad email address
    Join Date
    Jul 2005
    Posts
    172
    Post Likes
    Upss! I missed the set part!!!

    Anyways, reading my notes lineset "p" traps are

    used when condenser is installed higher than the

    evaporator, providing an aid in oil return back to the

    compressor. Most manufacturers now recommend to go down in

    line size instead of using "p" traps.

    I hope this help you a little!!!!!!!

  5. #5
    Join Date
    Nov 2001
    Posts
    1,874
    Post Likes
    Do a search you'll find many threads on this.
    If you try to fail, and succeed.
    Which have you done ?



  6. #6
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    And always follow the manufactures recommendations!

  7. #7
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    Most mfg's do not recommend them as mentioned. When you read about traps int eh suction, you are generally reading from an older text. As ha been pointed out, follow the mfg's recommendations.

  8. #8
    Join Date
    Feb 2001
    Posts
    472
    Post Likes
    Thread Starter

    Question

    igwt777, on a heat pump, half the time the condenser is installed higher than the evaporator, and for the rest of the year it's the opposite. How does that work?

  9. #9
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    ICP still recommends them on their units.

    The instruction manuals are very specific about how many and to the locations for different install requirements.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •