Results 1 to 9 of 9
Thread: line set trap
    Can somebody educate me on what a line set trap is for?
    igwt777 is offline Professional Member - T&B bad email address
    Jul 2005
    Refrigerant or condensate???
    Isn't a line set always for refrigerant?
    Jul 2005
    Upss! I missed the set part!!!
    Anyways, reading my notes lineset "p" traps are
    used when condenser is installed higher than the
    evaporator, providing an aid in oil return back to the
    compressor. Most manufacturers now recommend to go down in
    line size instead of using "p" traps.
    I hope this help you a little!!!!!!!
    Nov 2001
    Do a search you'll find many threads on this.
    Which have you done ?
    Apr 2003
    And always follow the manufactures recommendations!
    Most mfg's do not recommend them as mentioned. When you read about traps int eh suction, you are generally reading from an older text. As ha been pointed out, follow the mfg's recommendations.
    Question
    igwt777, on a heat pump, half the time the condenser is installed higher than the evaporator, and for the rest of the year it's the opposite. How does that work?
    Apr 2003
    ICP still recommends them on their units.
    The instruction manuals are very specific about how many and to the locations for different install requirements.