Can somebody educate me on what a line set trap is for?
-
07-13-2005, 08:00 PM #2
Professional Member - T&B bad email address
- Join Date
- Jul 2005
- Posts
- 172
Refrigerant or condensate???
-
07-13-2005, 08:14 PM #3
Regular Guest
- Join Date
- Feb 2001
- Posts
- 432
Isn't a line set always for refrigerant?
-
07-13-2005, 08:33 PM #4
Professional Member - T&B bad email address
- Join Date
- Jul 2005
- Posts
- 172
Upss! I missed the set part!!!
Anyways, reading my notes lineset "p" traps are
used when condenser is installed higher than the
evaporator, providing an aid in oil return back to the
compressor. Most manufacturers now recommend to go down in
line size instead of using "p" traps.
I hope this help you a little!!!!!!!
-
07-13-2005, 09:35 PM #5
Professional Member
- Join Date
- Nov 2001
- Posts
- 1,874
Do a search you'll find many threads on this.
If you try to fail, and succeed.
Which have you done ?
-
07-13-2005, 10:46 PM #6
Grumpy Old Man
- Join Date
- Apr 2003
- Posts
- 6,383
And always follow the manufactures recommendations!
-
07-13-2005, 11:34 PM #7
Most mfg's do not recommend them as mentioned. When you read about traps int eh suction, you are generally reading from an older text. As ha been pointed out, follow the mfg's recommendations.
-
07-13-2005, 11:47 PM #8
Regular Guest
- Join Date
- Feb 2001
- Posts
- 432
igwt777, on a heat pump, half the time the condenser is installed higher than the evaporator, and for the rest of the year it's the opposite. How does that work?
-
07-13-2005, 11:55 PM #9
Grumpy Old Man
- Join Date
- Apr 2003
- Posts
- 6,383
ICP still recommends them on their units.
The instruction manuals are very specific about how many and to the locations for different install requirements.