    I installed a txv valve in an air-handler and i did not remove the fixed metering device since i did not see how the distributor would evenly distribute the gas to 6 different tubes with-out the oraface installed. I know in the supermarket systems the txv needs a nozel before the distrubutor. I had 8 degrees superheat and 20 degrees sub-cooling with it still in place, do you think i will have any trouble?
    Quality and Value Service and Repair

  2. #2
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,849
    Post Likes
    You need to remove the piston unlees it is .100 or bigger. The MD will give too much of a restriction. Rheem is the only unit I know of that gives a big piston to replace original one.
    Karst means cave. So, I search for caves.

  3. #3
    Join Date
    Jul 2001
    Location
    Fairfield and NewHaven Counties in Commecticut
    Posts
    4,982
    Post Likes
    Thread Starter
    I still do not believe if i removed the piston i would have even flow to all distributor tubes

    Maybe i will get a few 100 pistons for this purpose.
    Quality and Value Service and Repair

  4. #4
    Join Date
    Jan 2004
    Location
    Location: Tulsa Oklahoma
    Posts
    222
    Post Likes
    What did the instructions with the TXV say. I've never seen
    a retro-fit TXV kit for air-conditioning coils that didn't
    require removal of the orifice. What brand airhandler do you
    have there?
    Whoa Maynard - that's not how it works.

  5. #5
    Join Date
    Jan 2005
    Posts
    48
    Post Likes
    Just my two cents...but why meter a metering device? A proper working TXV will run 10-15 s/h, you just added basically a restriction condensing more liquid into the coil and back at your compressor...so future problems. Charge TXV's by s/c but get rid of the orifice first.

  6. #6
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,849
    Post Likes
    Go to the rheemote site and look up the size piston that is needed for the tonnage. It is not .100 I just threw a number out there.


    Search in pro section for a password I posted for Rheemote.
    Karst means cave. So, I search for caves.

  7. #7
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,849
    Post Likes
    I looked it up for you.

    Ton Piston

    1.5 .099
    2 .120
    2.5 .140
    3 .157
    3.5 .157
    5 .172

    This is for Rheem, other manuf. may difer.
    Karst means cave. So, I search for caves.

  8. #8
    Join Date
    Jan 2005
    Posts
    48
    Post Likes
    Im a Rheem dealer and just did a a/h same situation, they dont sell a 12 seer a/h only 10...need to add/braze in a TXV kit that came with a (think 89 orfice) thought it was odd and called my rep....no answers so chucked the orifice, thing dialed in perfectly s/c 10 s/h 12. Never with any other brand have i had to use a orifice with a TXV.

  9. #9
    Join Date
    Jun 2001
    Location
    Tx
    Posts
    3,917
    Post Likes
    This idea may be up for discussion. I would think that since the low pressure side of the coil (circuits) would be an equal pressure drop compared to the high side, that there would be an equal 'pulling' effect of the refrigerant into all of the feeders.

    The only exception I can see is if you have a blocked feeder, one having a longer circuit than another, or a distributer header that is causing more to flow in one than the other due to the placement of the feeders in it.

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    If you left a metering orfice in, your defeating most of the ability of the txv.

    Rheem uses a blancing orfice with a txv, not a regulating orfice.

    Did you check the amp draw.


  11. #11
    Join Date
    Jul 2001
    Location
    Fairfield and NewHaven Counties in Commecticut
    Posts
    4,982
    Post Likes
    Thread Starter
    The manufacturer did not rate the coil for a TXV. The valve did work and the main reason i installed a valve was to prevent flooding (zoning), which it will do fine, thanks men! I installed a non-oem sporlan!
    Quality and Value Service and Repair

  12. #12
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    Originally posted by jaxman
    Im a Rheem dealer and just did a a/h same situation, they dont sell a 12 seer a/h only 10...need to add/braze in a TXV kit that came with a (think 89 orfice) thought it was odd and called my rep....no answers so chucked the orifice, thing dialed in perfectly s/c 10 s/h 12. Never with any other brand have i had to use a orifice with a TXV.
    Apparently your rep doesnt carry it or you are not buying them but they make the BHC which can be ordered with a piston or TXV which matches with the 10 and most 12 SEER stuff, the BHK which is generally used in 12-14 SEER applications. Then the BHL, the BHM and the BHN. You're pretty much covered from 10-18 SEER. Maybe you need to revisit the spec sheets.

    The orifcace is used as a distributor when the TXV is installed. If you install it from a kit you need to replace the exsisitng piston with the new one. Now, in an upflow application you may find it doesnt make alot of difference in many cases but in a counterflow or horizontal, it can make a big difference.

    As for other brands, they also dont have as many circuits in their evaps as the multiflex has therefore they dont ned to address it quite the same. Sometimes I wonder why so many contractors want Rheem to copy other mfg's coil designs or want the air handlers to be larger when space constrants call for a low profile design. There is a reason for just about everything regardless of the brand.

  13. #13
    Join Date
    May 2007
    Location
    Dry as a bone Tucson
    Posts
    4,866
    Post Likes
    Quote Originally Posted by docholiday View Post
    Apparently your rep doesnt carry it or you are not buying them but they make the BHC which can be ordered with a piston or TXV which matches with the 10 and most 12 SEER stuff, the BHK which is generally used in 12-14 SEER applications. Then the BHL, the BHM and the BHN. You're pretty much covered from 10-18 SEER. Maybe you need to revisit the spec sheets.

    The orifcace is used as a distributor when the TXV is installed. If you install it from a kit you need to replace the exsisitng piston with the new one. Now, in an upflow application you may find it doesnt make alot of difference in many cases but in a counterflow or horizontal, it can make a big difference.

    As for other brands, they also dont have as many circuits in their evaps as the multiflex has therefore they dont ned to address it quite the same. Sometimes I wonder why so many contractors want Rheem to copy other mfg's coil designs or want the air handlers to be larger when space constrants call for a low profile design. There is a reason for just about everything regardless of the brand.
    Because bigger coils have a lower pressure drop..........................................and are easier to clean.....................the multiflex totally sucks in all of it's design aspects, a complete POS......................I have also found that the piston becomes a restricter in an upflow application.............
    "I aint going to spit on 30 years of my life" Monte Walsh


Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •