    Had a service call last week...A/C split tripping breaker.
    Suction head pressure OK,
    SH & SC OK,
    Air flow OK,
    Amperage draw OK,
    Megger readings OK,
    Customer NOT playing with T stat OK,

    2 days later compressor blew...
    relace whole unit under warranty, compressor not available

    1 day later breaker keeps tripping

    installed a time delay before the contactor and set for 5 minutes...

    everything now works great..

    this is an FYI posting.., hope it helps

  2. #2
    Join Date
    Jan 2005
    Posts
    340
    Post Likes
    Originally posted by key
    Had a service call last week...A/C split tripping breaker.
    Short cycling? Make and model of thermostat?

  3. #3
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,481
    Post Likes
    sounds like the problem is still there.....the time delay just prevents the short cycle.
    If everything was always done "by the book"....the book would never change.

  4. #4
    Join Date
    Nov 2001
    Posts
    1,874
    Post Likes
    Weak breaker or loose wires.

    Did you pull the panel cover to check for a good conection ? Or hot breaker ?

    Just my 2 cents.
    If you try to fail, and succeed.
    Which have you done ?



  5. #5
    Join Date
    Apr 2005
    Location
    Richmond, Virginia
    Posts
    365
    Post Likes
    Who manufactured the equipment?

    I'd have to agree with smokin68--sounds like problem is still there. I've seen a few units that trip because of a loose wire at the breaker.
    Sean Cantrell

  6. #6
    igwt777 is offline Professional Member - T&B bad email address
    Join Date
    Jul 2005
    Posts
    172
    Post Likes
    You said time delay "fixed" the problem. My guess is that your problem still there. Are you shure system is not short cycling?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.