Results 1 to 6 of 6
    South/West of Quebec in the other part of Canada
    Had a service call last week...A/C split tripping breaker.
    Suction head pressure OK,
    SH & SC OK,
    Air flow OK,
    Amperage draw OK,
    Megger readings OK,
    Customer NOT playing with T stat OK,
    2 days later compressor blew...
    relace whole unit under warranty, compressor not available
    1 day later breaker keeps tripping
    installed a time delay before the contactor and set for 5 minutes...
    everything now works great..
    this is an FYI posting.., hope it helps
    Short cycling? Make and model of thermostat?
    sounds like the problem is still there.....the time delay just prevents the short cycle.
    Nov 2001
    Weak breaker or loose wires.
    Did you pull the panel cover to check for a good conection ? Or hot breaker ?
    Just my 2 cents.
    Which have you done ?
    Apr 2005
    Richmond, Virginia
    Who manufactured the equipment?
    I'd have to agree with smokin68--sounds like problem is still there. I've seen a few units that trip because of a loose wire at the breaker.
    Sean Cantrell
    igwt777 is offline Professional Member - T&B bad email address
    Jul 2005
    You said time delay "fixed" the problem. My guess is that your problem still there. Are you shure system is not short cycling?
Quality Home Comfort Awards
