Had a service call last week...A/C split tripping breaker.
Suction head pressure OK,
SH & SC OK,
Air flow OK,
Amperage draw OK,
Megger readings OK,
Customer NOT playing with T stat OK,
2 days later compressor blew...
relace whole unit under warranty, compressor not available
1 day later breaker keeps tripping
installed a time delay before the contactor and set for 5 minutes...
everything now works great..
this is an FYI posting.., hope it helps
-
Originally posted by key
Had a service call last week...A/C split tripping breaker.
Short cycling? Make and model of thermostat?
-
sounds like the problem is still there.....the time delay just prevents the short cycle.
If everything was always done "by the book"....the book would never change.
-
Weak breaker or loose wires.
Did you pull the panel cover to check for a good conection ? Or hot breaker ?
Just my 2 cents.
If you try to fail, and succeed.
Which have you done ?
-
Who manufactured the equipment?
I'd have to agree with smokin68--sounds like problem is still there. I've seen a few units that trip because of a loose wire at the breaker.
Sean Cantrell
-
You said time delay "fixed" the problem. My guess is that your problem still there. Are you shure system is not short cycling?