Thread: the Low is Hi
    Hi everyone,
    need some help,split system 2.5 ton the condensing unit
    is clean so is the evap coil and the indoor blower.
    The outside temp is 93F,suply air 67F return
    air 80F hi side psi 220 lo side psi 90 psi,
    Where would be the problem since the low side
    is at 90psi?
    thanks for any help.
    leland nc
    may not be a problem
    heavy load and the suction presure may drop to normal as the inside load drops
    Nov 2000
    Eastern PA
    Sounds like an oversized metering issue. At those load conditions the head is also low. What are the condensing unit and indoor coil models?
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV
    Dec 2003
    Location!, Location!
    R-22?
    93°F and 220 psi? kinda low
    67°F and 90 psi?
    low charge and vapor at the restrictor or wrong size restrictor?
    ÄT = 13°
    What are the superheat and subcooling
    We ALWAYS need the superheat and subcooling. Without them, we can't even make an informed guess about what the problem is...
    Knowing what type of metering device the indoor coil has is handy info too.
    Florida
    Once you get that superheat and subcool measurements,you have to check that airflow.....13 degree delta t is way low.Busted ductwork,wrong fan speed,etc.
