Results 1 to 7 of 7
    I'm hoping someone can help with a decision my tech and I are trying to make...for a 5-ton American Standard split system, what is the smallest diameter copper tubing that would be acceptable for the low pressure side fo the lineset? 1" or 7/8"? The distance between the evap coil and the condenser is approx 30 feet.
    atlanta
    7/8 will be ok but 1 1/8 is preferred.
    Jul 2003
    ALABAMA
    I agree 1 1/8. But 7/8 should work for 30 feet.
    Tyler, TX
    If this is new construction, or accessable for changeout, then use the larger tube.
    The 7/8 will work, but I'm pretty sure there must be a good reason for the larger size being recommended by the manufacturer.
    Noise?
    Efficiency?
    Sale on 1 7/8" service valves?(I doubt it.)
    RSES Certificate Member Specialist
    Southwest Regional Association of RSES Secretary, 2017
    Check the mfrs data,their may be a small capacity loss as well.
    make sure to use a longthrow copper 90's where needed. i use longthrows on anything bigger than 5/8
    It may require the 1 1/8" to get its seer rating.
    Read the install manual and use what it recommends.