Results 1 to 5 of 5
  1. #1
    Join Date
    Oct 2008
    Posts
    52

    First solo boiler with h2o tank

    Not the best picture....be gentle.
    Attached Images Attached Images  

  2. #2
    Join Date
    Sep 2008
    Posts
    500
    insulation?

  3. #3
    Join Date
    Feb 2011
    Location
    Michigan
    Posts
    37
    What size piping is on the IDW loop? What is the head loss of the boiler? Looks like you have 3 007's in there, whose IDW tank is that? Piping work looks good. Can't see the expansion tank. Doesn't appear that your pumping away. It appears that the IDW pump is too small and possibly the others depending on the head loss for those zones. What size solo is it?

  4. #4
    Join Date
    Jan 2007
    Location
    NH
    Posts
    228
    looks like its pumping towards - bad, bad
    air vents on each pump - pump will suck air in. Spirovent on supply is all you need.
    where is expansion tank, LWCO, flow check valves,

  5. #5
    Join Date
    Feb 2011
    Location
    Michigan
    Posts
    37
    I really appreciate the nice work, but all that can be for naught. A simple reading of the manual will tell you the recommended way of near boiler piping and thats not it. Also the head loss of the solo says the 007 is too small unless that is a 60k unit. I would like to know the heater brand because I'm pretty sure its supposed to have 1" piping ( even tho the tappings are 3/4) and calls for a larger pump, even tho the solo has a better head loss than other mod cons.