    Thanks again to all who responded,especially Mark B..After evaluating all responses,I was pretty sure the dual run capacitor was bad.I removed capacitor and upon inspection,noticed the case was "bulged".I am fairly confident that this is the problem.
    Thank You Again,AL

  2. #15
    Join Date
    Jul 2005
    Posts
    4
    I replaced the dual run capacitor and all is well.
    Thanks Again,AL

  3. #16
    Join Date
    Jul 2005
    Posts
    6
    If your breaker is tripping you probably have a short to groud.

  4. #17
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,856
    Originally posted by davidt
    If your breaker is tripping you probably have a short to groud.
    Actually the cap was probally shorted, not the compressor.
    Karst means cave. So, I search for caves.

  5. #18
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    Originally posted by davidt
    If your breaker is tripping you probably have a short to groud.
    If the breaker is weak, or is the minimum to meet the MCA requirements for the unit, it is common for the breaker to trip before the internal overload on the compressor trips when the compressor is unable to start.
    If more government is the answer, then it's a really stupid question.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event