Results 14 to 18 of 18
    Jul 2005
    Thanks again to all who responded,especially Mark B..After evaluating all responses,I was pretty sure the dual run capacitor was bad.I removed capacitor and upon inspection,noticed the case was "bulged".I am fairly confident that this is the problem.
    Thank You Again,AL
    Jul 2005
    I replaced the dual run capacitor and all is well.
    Thanks Again,AL
    Jul 2005
    If your breaker is tripping you probably have a short to groud.
    Grottoes VA
    Actually the cap was probally shorted, not the compressor.
    If the breaker is weak, or is the minimum to meet the MCA requirements for the unit, it is common for the breaker to trip before the internal overload on the compressor trips when the compressor is unable to start.
    RSES Certificate Member
    RSES-SWRA President