Thread: Humidistat for Bryant Systems?

  1. #1
    Join Date
    Feb 2005
    Posts
    20
    Post Likes

    Thermidistat for my Bryant systems?

    Hi there,

    My wife and I just bought a 1927 house that is set up with 2 zones -- a Bryant 697C heat pump for the 2nd floor and a 350MAV furnace / FK4C & 597C coil and condenser for the first floor. After about 2 weeks in the house, we've noticed that the humidity levels in the house are higher than we'd like, and are interested in upgrading the thermostats as well, which are the cheapest Bryant-labeled manual thermostats that seem to exist.

    I know that Bryant sells a Thermidistat product, which would give us the programmability and humidity controls we're interested in, but was wondering if anyone knows if they are appropriate/compatible with these pieces of equipment.

    Thanks for your help-

  2. #2
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Will work with the FK air handler,and I tink,not sure,the MAV,thinking is the same as the Carrier,MVP.

    Someone will know for sure on the furnace.

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    The 350MAV is the generic single stage 90. I don't think the Thermidistat will help with dehumidifying will it?

    Make sure blowers are set to no more than 400 CFM/ton and don't run the blower constantly.

  4. #4
    Join Date
    Feb 2005
    Posts
    20
    Post Likes
    Thread Starter
    Thanks for the replies. I know that listing the furnace is overkill... I just wanted to make sure I was clear that the FK4C & 597C was paired up with the furnace and that it would all play together nicely with the new thermostat choice.

    I was under the impression that the Thermidistat would control the systems to run longer to remove additional moisture based on the settings we're looking for. Am I wrong about this?

    Thanks again.

    [Edited by Spunkmeyer on 07-09-2005 at 11:51 AM]

  5. #5
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    FK4c ,is an air handler ,can't be paired up with a furnace.


    The indoor unit,furnace or air handler ,needs to have a variable speed indoor motor ,te air handler does ,and the furnace doe not.

    However ,our Service Mgr ,has a Thermidistat on a non-variable speed in his home,using high speed for normal,and med on a call to dehumidify and has exceelant results.

    Some of the Carrier literature shows this setup,with a PSC(standard motor),so suggest that to your contractor.

  6. #6
    Join Date
    Feb 2005
    Posts
    20
    Post Likes
    Thread Starter

    Oops!

    My error - the FK4C is paired with the 697C.

    Thanks for the help... dash, it sounds like we'd get more from the FK4C/697C combo having a Thermidistat because of the variable speed capabilities of the FK4C than we would by the 597C and the 350MAV.

  7. #7
    Join Date
    Nov 2004
    Posts
    2,928
    Post Likes
    Originally posted by dash
    results.

    Some of the Carrier literature shows this setup,with a PSC(standard motor),so suggest that to your contractor.
    form number?

  8. #8
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    tstat-2w & tstat-23si

  9. #9
    Join Date
    Nov 2004
    Posts
    2,928
    Post Likes
    thanks,im experimenting and that may be helpful.

  10. #10
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Originally posted by jrbenny
    tstat-2w & tstat-23si
    Thanks benny,

    No literature at home.

    Note:

    With a PSC motor,check the ESP and the fan chart,to insure minimum cfms on the lower speed chosen,for dehum..

  11. #11
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    This can help with a standard PSC motor set-up.

  12. #12
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Originally posted by jultzya
    This can help with a standard PSC motor set-up.

    We tried them and without a new ball bearing motor,very noisey.

    How did they work for you?

  13. #13
    Join Date
    Nov 2004
    Posts
    2,928
    Post Likes
    Originally posted by dash
    With a PSC motor,check the ESP and the fan chart,to insure minimum cfms on the lower speed chosen,for dehum..
    Ok.the experiments are done with subjects from the ac graveyard..they died without leaving fan data or model numbers...

    but that is good reminder

    thanks all.

  14. #14
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Originally posted by dash
    How did they work for you?
    I have personally never used one, but know of others that have had success with them.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •