    Last question:

    If I only stick my electronic manometer at the inlet of the furnace (before the filter)- and I get (-0.10"w.c.) reading, is that a usefull info ? Does it tell me anything at all ?

  2. #22
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    It tells you that the filter/return duct system is in good shape.

  3. #23
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    It tells you that the ESP of the return system excluding the filter is .1,which if "all else is well",say it's a new system on the correct fan speed, the return is fine.


    The filter,coil,etc.,as mentioned before could be clogged,which reduces cfms,which lowers duct system static.