    Quick question to the pros. If you need 48K BTUs based on a load calculation ( say at 95F outside/75F inside ) design point, do you put in a 4 ton condensor or a 5 ton condensor? My point is a 4 ton condensor probably doesnt produce 4 tons at those design temperatures, it may very well be 3.5 tons. In other words, "4 tons" may be a marketing number ( or does does produce 4 tons but not at 95/75 design temperatures). Do you guys look at the actual capacity at your design temps when choosing equipment or just go with the "marketing" number?

  2. #2
    Join Date
    Apr 2004
    Posts
    7,680
    The spec sheets or product data sheets give you tha actual capacities at ARI conditions. Generally that is pretty close to design. Dont assume 4 tons is 48,000. And more importantly make sure your unit matches the sensible and latnet load of the house, not nessesarily the total load.

  3. #3
    Join Date
    Jul 2004
    Posts
    253
    Originally posted by docholiday
    The spec sheets or product data sheets give you tha actual capacities at ARI conditions. Generally that is pretty close to design. Dont assume 4 tons is 48,000. And more importantly make sure your unit matches the sensible and latnet load of the house, not nessesarily the total load.
    Hi Doc, yes, that is my point - a "4 ton unit" is probably not 4 tons at 95/57 temps. In that case, you would more likely put in a "5 ton unit" since it is closer to 48K BTUs while not being less than 48K BTUs ?

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,331
    As doc said you need to check the product spec sheets.

    By changing which indoor coil is matched to the outdoor, you can get more or less btu's.

    Some coils are high sensible, others are higher latent.

    Manual S will help with deciding what size and what match up to use.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Load is 48,000 at 95 outdoor,75 indoor.


    ARI is at 80°F indoors.To convert to 75°F,835 sensible btus ,times 5° difference,time 1.6,equals a deduct of 6,680 btus,gonna need 5 tons.

    The deduct is per 1000 cfms ,so 1600/1000= the 1.6

    Some mfrs sheets have "other" indoor specs,but 80° is the most common.