    OK, this is my first post and it could get long. I have worked on many auto a/c units and have had the air conditioning/refrigeration school in the Navy. I don't consider myself a pro by any means, but probably know enough to be dangerous.

    The problem: the condensing fan froze on my Carrier Unit. No Problem I tell my wife. I can fix it! I go to Grainger to get a new motor and they don't have a 1/5 hp motor. The salesman says that a 1/4 hp at the same PRM will work just fine. Off I go with my NEW motor.

    Do the change, everything is working and I'm sooo proud of myself. Ten minutes later, the condensing fan motor stops. I had just finished mowing the grass and was blowing of the patio, so decided to use the blower to cool the motor. After a short period of cooling, was able to restart the Unit.

    Gave Grainger a call to complain and the NEW salesman asks about the capacitor. Did I change it? I tell him yes. Grainger didn't have a 60/7.5, so the Grainger salesman sent me to Johnstone. I got a new 60/7.5 from Johnstone and installed it.

    The New salesman tells me that THAT is what the problem is. This motor takes a 5 mfd not a 7.5 mfd. Would that make that much of a difference?

    I go to Grainger to get a 60/5 mfd capacitor and they don't have one. They tell me to use the 60 on the dual and wire up a single 5 mfd for the fan motor.

    I did all this and the condensing fan motor is running just fine. UNTIL...it's Saturday and I'm at work, 65 miles from home and my wife calls and the A/C is out. Now what do I do??? I started making calls and everyone can make it out on Monday afternoon. Now, living in Phoenix at this time of year, this is NOT an option.

    I finally found a company that would send someone out for a $69.95 call charge. I was actually happy about this. I then started worrying about the wife having to deal with this guy. It is not an easy thing for me to leave work, but I was able to work it out and got to my house before the Tech.

    I explained the whole story to him, so he checks the running current on the motor. It's running 2.2 - 2.25 amps. The motor plate rates it at 2.2-2.3. He tells me the new motor is BAD. He says that the plate rating is the max rating and that is why it is over heating the motor. Ok, red flag rises. He then hooks up his gauge set and informs me that my unit is short. He would need to add some freon to it. Another red flag!

    Oh, I say. How short is it??? He tells me that the suction pressure is running at 50# and it should run at 70#. It's 108 degrees with 7% humidity and this guy is telling me that he knows all this by just checking the suction pressure.

    I was so happy to get a Tech on Saturday afternoon, I decided not to give him any grilling and let him charge the unit. So I wrote him a check for $150 and he went away and I still had motor problems.

    I pulled the motor and went to Grainger to exchange it. Been a week now and the new motor has never tripped. I figure that maybe the thermals on the first motor may have been weak.

    Thanks to everyone that took the time to read this book that I just wrote. Should I call this company again when I need work, or should I find someone else????

    prein

  2. #2
    Join Date
    Apr 2002
    Location
    Dallas TX
    Posts
    2,216
    Get established with a company and have them do the maintenance. Alot of times having a compnay with a maint contract will get you preferred services with no OT. A tech can not tell exactly how low it is just by looking at it but seeing 108 out side and 50# suction is a definite sign that there is a problem in the refrigerant side of your system. Sounds like you are definitely dangerous and that is why you had such a drag around on your problem. Painful and possibly costly lesson but you know now I bet and won't make alot of those mistakes again.

    Congratulations on your enlightenment.

  3. #3
    Join Date
    Jul 2004
    Location
    Fort Lauderdale, FL
    Posts
    456
    Wow 69.95 for a Saturday call. Thats cheap, my straight time rate is 72.50.
    How much is it an hour?

  4. #4
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,744
    probably wiped out the motor from capacitor that was 50% to large. did service guy find leak or just top er off??
    saturday call wayyyy over those numbers

  5. #5
    Join Date
    Mar 2005
    Location
    Suppy NC
    Posts
    4,513
    as far as the motor goes. it is not that uncommon for them to come defective. may have been dropped or stacked to high
    or just sitting to long and the bushings tightened up.
    as far as freon 50# does seem a little light at 108 degrees. i wasnt there so who knows what was the high side and superheat did he check them. i think it was a good call on your part to call someone and let them do thier job. you also found out about the motor also so it worked in your favor all the way arround. 108 man that is hot

  6. #6
    Join Date
    Jul 2001
    Location
    Anderson,SC
    Posts
    997

    Hmm

    Did you check the rotation? The higher amp draw sounds like wrong rotation.


    STUD

  7. #7
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,189
    What's the model # of the A/C?

  8. #8
    Join Date
    Apr 2004
    Posts
    7,680
    The original one was probably off on its thermal overload too, or failed as a result of the heat. At that outdoor temp, I would have expected it to pull full amps and cleaned the outdoor coil. The slightes dirt would make that coil very hot.

    The tech is right 50 psig is low, especially for 108. And frankly if the unit was off and it was hot in the house 70 would be low too, but without details I cant say it needed refrigerant.

    I dont think he did you wrong, he probably copped an attitude when he found out you already tried to fix it and didnt want to come out and say you might have wasted your money. Sure use them again if you need em. After all not all companies will send a tech out to a non-customer on a saturday.

  9. #9
    Join Date
    May 2004
    Posts
    475
    Originally posted by docholiday
    After all not all companies will send a tech out to a non-customer on a saturday.
    Especially at that price rate.

  10. #10
    Join Date
    Jun 2005
    Posts
    2
    Wow, thanks everyone for the replies.

    Yes, the rotation was correct. I am really glad that this guy sounds all right. We talked quite abit and he was an enjoyable person.

    I had no idea of what rates are being charged. Sounds like that was VERY reasonable. On my side anyway.

    Model of Carrier is 38BRB048320.

    No leak was repaired. Only topped off the charge.

    I really feel that the whole problem was weak thermals. The original motor, the bearings were frozen.