    Tempstar Fan Relay

    Hey guys, just moved into a house a couple weeks ago and started to notice that the blower on this Tempstar furnace stays on even after the Honeywell stat clears the "Cool on" or "Heat on" condition. Read up on it, people said try hitting the side of the furnace or finding the relay and tapping on it, so I did, and when I hit the front of the furnace near the relay on the housing it shuts off. Is that a good indication of a bad relay? lol

  2. #2
    Join Date
    Feb 2011
    Location
    North East Ohio
    Posts
    786
    Call a tech to find out for sure

  3. #3
    Join Date
    Apr 2010
    Location
    Arizona
    Posts
    192
    Quote Originally Posted by jsimonye View Post
    Hey guys, just moved into a house a couple weeks ago and started to notice that the blower on this Tempstar furnace stays on even after the Honeywell stat clears the "Cool on" or "Heat on" condition. Read up on it, people said try hitting the side of the furnace or finding the relay and tapping on it, so I did, and when I hit the front of the furnace near the relay on the housing it shuts off. Is that a good indication of a bad relay? lol
    The question I need to ask is: Does it stay on all the time or does the fan run for up to 2 minutes and then shut down on it's own? If it runs continuously, you need a technician and if it runs for a couple of minutes and shuts down on it's own, this is normal operation and not a problem.
    I would remind you that extremism in the defense of liberty is no vice! And let me remind you also that moderation in the pursuit of justice is no virtue!

    The late and greatest ever, Senator Barry Goldwater

  4. #4
    It runs continuously, or until I "manually shut it off". I'm gonna have the wife call a technician tomorrow I suppose. Are the relays universal (other then different voltages)?

    Edit: I forgot to mention though, it will sometimes shut off itself, it's like a 50/50 thing. Sometimes it'll stay on for 20 minutes after the system shuts down, other times it'll shut off right when the system shuts off down. That's what made believe it was a sticky relay.
    Last edited by jsimonye; 04-10-2011 at 04:47 PM. Reason: Forgot something.

  5. #5
    Join Date
    Apr 2010
    Location
    Arizona
    Posts
    192
    Quote Originally Posted by jsimonye View Post
    It runs continuously, or until I "manually shut it off". I'm gonna have the wife call a technician tomorrow I suppose. Are the relays universal (other then different voltages)?

    Edit: I forgot to mention though, it will sometimes shut off itself, it's like a 50/50 thing. Sometimes it'll stay on for 20 minutes after the system shuts down, other times it'll shut off right when the system shuts off down. That's what made believe it was a sticky relay.
    Only )our tec can answer that for you. Good luck and I hope it all comes out good for you!
    I would remind you that extremism in the defense of liberty is no vice! And let me remind you also that moderation in the pursuit of justice is no virtue!

    The late and greatest ever, Senator Barry Goldwater

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event