07-09-2005, 02:04 PM #27Remove compressor, invert for a few hours.Originally posted by jrc2905
Could someone list what is the procedure is for removing the oil from a hermetric compressor?
-
07-09-2005, 08:10 PM #28
Professional Member
- Join Date
- Sep 2004
- Posts
- 172
ravenx you a vorhees or johnstone guy?
-
07-10-2005, 10:08 AM #29
Professional Member
- Join Date
- Aug 2002
- Posts
- 391
"Could someone list what is the procedure is for removing the oil from a hermetric compressor?
Drill a hole in the bottom of the compressor"
How do you get your drill "under" the compressor?
LOL
[Edited by jrc2905 on 07-10-2005 at 10:16 AM]The obvious is obvious
-
07-10-2005, 07:18 PM #30
I found sticking a 1/4" plastic tube down in through the suction port into the bottom of the compressor and then sticking another just inside the suction port. Seal around both and blow nitrogen (slowly, very slowly) through the one that you put in second. The pressure will force the oil out the other one. make usre you collect it into a container as mentioned to recharge it with the same amount of new oil.
-
07-10-2005, 07:32 PM #31doc that has to be the easest and most intelagent ways i have heard ofOriginally posted by docholiday
I found sticking a 1/4" plastic tube down in through the suction port into the bottom of the compressor and then sticking another just inside the suction port. Seal around both and blow nitrogen (slowly, very slowly) through the one that you put in second. The pressure will force the oil out the other one. make usre you collect it into a container as mentioned to recharge it with the same amount of new oil.
even though i only done it 2 times. if i ever have to change the oil in a resi unit i will try this
thanks