    I'm trying to use a W7751G1003 actuator purely with 24 volts to drive it open and closed. I've taken the Excel board off and have RWWG for wires, thinking that R is hot and the two W's are common for power open and power closed. However, either that is not the case or I have a dead actuator. Or, the G wire figures in there somehow. While I understand the actuator is an ML6161, I don't know if special changes were made for the Excel module. The sticker shows 20-30VAC Rating, but that might be for the board to process. If anyone knows, I'd appreciate it.

  2. #2
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,051
    Post Likes
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

  3. #3
    Join Date
    Dec 2004
    Location
    SE Penna.
    Posts
    61
    Post Likes
    The ML6161 actuator is a floating actuator (drive open/drive closed) and uses Red for clockwise rotation, Green for counterclockwise and the whites are common.