    I installed a 12 Seer 38BRC036, enhanced coil, V speed furnace, short line set (8' tops). Charged SC method. Compressor is cutting out in internal over load. Any ideas

  2. #2
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Post all the needed data for a competent answer to your question.

    Model number __
    Metering device __

    SP __ /T __ LP __ /T __
    ST __ LT __
    SH __ SC __
    AT __ CT __
    IWB __ IDB __
    Evap ST __ LT __
    Comp A __ Rated A __

    Have any pictures that you can post?

  3. #3
    Join Date
    Sep 2004
    Posts
    3,157
    Post Likes
    If the comp is kicking off on the internal overload , will he be able to take all of the required readings , temps , pressures?


  4. #4
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Well he doesn't say how quick the compressor kicks out, but I'd hope it would take 'awhile' beings its a new install.

    He'd have to have something...?

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    69,748
    Post Likes
    With an 8' line set, You usually have to take some gas out.

    Did you leave it run for 15 minutes before checking the charge.

    If it won't run long enough to get the readings. Take some gas out, and try again.


    May have to recover, and weigh charge back in, minus the difference of the line set, and precharge length.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech365 Virtual Event