    First time post to this forum, so hello all!

    At one of our sites we have a 400 ton RTHC, water cooled that has had a history of running oil loss problems. We have checked oil sensor, charge, master oil solenoid, oil filter(s), etc.,. I don't have it with me but every item in the IOM manual for running oil has been checked. The chiller will run for a week, a month, 2 months and then go down.
    This last Sunday we had another shut down on oil. When I arrived, I checked the oil sump level, 7". Trane says 2-6" is good. I set up my VOM on the optical oil sensor and started the machine. It started up fine, with a .24VDC optical oil signal. It ran about 10 minutes. I then heard a click and a slight clunk from the pueblo loop (oil filter area), the optical oil signal immediately went to 19.89VDC(never saw that happen), and the machine shut down in 5 seconds on running oil loss. When I looked thru the optical oil sensor site glass, the line appeared empty.
    _____________________________
    Per Trane Service Bulletin:
    0-2VDC = wet reading (all oil optically sensed)
    2-20VDC = foam optically sensed
    >10VDC = after delay, will shut down chiller on running oil loss
    *these values are from memory, correct me if needed
    _____________________________

    I thought it was the master oil solenoid dropping out. I got another pair of eyes on the job. we set up min/max VOM's across the pressure switch and starter contacts that could drop out the k400 contactor that would close the master oil solenoid, drain the pueblo loop, and dump the machine. We ran the machine and the problem never reoccurred. The chiller has been running since.
    Has anyone had oil problems like this on an RHTC?
    Is there any do's and don'ts any one can pass along on this type of machine?
    Yes, I am planning on going to an RTHC class this winter. But we gotta get thru this problem first.

    Readings:
    CHW Setpoint = 42*
    Tower Water Setpoint = 78* Low Speed, 82* Hi Speed
    Discharge Superheat = 18-26*

    Cond Approach = 2* - I know, a little low. But we recently found another chiller connected to the loop that has a evap to chw refrigerant leak. The chw had a lot of foam in it(glycol protected) and I don't think the evap on the RTHC was loaded as good as it is now. Previously, at setpoint, we ran 22-28% loaded and now that we've isoloted the other chiller and bled the system, we are running 38-44% loaded at setpoint. Anyway, my next visit I'll add some 134a.

    Evap Approach = 6* - Another variable as the other chiller is tee'd into the RTHC chiler's supply with a B&G Flow Setter in between each to cause a pressure drop to feed the other chiller. Real down and dirty and another brilliant engineering cost cutter. Bottom line, I'll have to check flow thru the RTHC to verify where it's at right now.

    Suction = 33#
    Discharge = 103#

    Any help on this issue would be greatly appreciated. Our backs are to the wall as the other chiller down for evap repairs right now is our backup to this chiller. Without it, a good part of the campus is without chilled water.
    TIA for all replies,
    Jogas

  2. #2
    Join Date
    Aug 2000
    Location
    Under my tree
    Posts
    5,133
    Post Likes
    Cant help you out but its a very good post, full of information. Wait till you read some of the crap these other posters post and expect to get help on.
    To much work with too little time!!!!

  3. #3
    Join Date
    Dec 2004
    Location
    Work Primarily Downtown Chicago Loop Area
    Posts
    22
    Post Likes
    I think you are on the right path with your diagnosis. You stated you heard a noise that might be consistent with a contactor or solenoid if I understood you correctly shortly after the noise your safety tripped on what seems to be a true loss of oil from the optical.. Try using circuit monitors across your possable trip points that would take out your oil flow.. ( The kind that you can leave on site and not miss if they grow legs ). Good luck and post back when you find it.

  4. #4
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,780
    Post Likes
    Thread Starter
    The RTHC has not dropped out again since my last post.
    I was at the job working on the other chiller and added 120# to the RTHC in an effort to raise my condenser approach. The condenser approach stayed at 0*, and the evap approach dropped from 6* to 3*. Sub-cooling ended up at 5*.


  5. #5
    Join Date
    Sep 2002
    Posts
    525
    Post Likes
    Originally posted by absrbrtek
    Cant help you out but its a very good post, full of information. Wait till you read some of the crap these other posters post and expect to get help on.
    Abs,

    You are killing me!!

  6. #6
    Join Date
    May 2005
    Location
    puget sound, seattle
    Posts
    25
    Post Likes
    like the specifics of your post, I wish they were mostly that good. I have had intermittent problems like this maney times. I use a tattletail, either bought or I make up my own using a fuse holder and a 200ma amp fuse matching the voltage of the circut your on. fuses rt radio shack or any electronic supply houses.

  7. #7
    Join Date
    Jul 2005
    Posts
    5
    Post Likes
    think about your approaches 2 on cond 6 cooler you sound like you could be low on charge I had from fact low on charge and as your load changes oil return could be a problem also raise water to 44or 45

  8. #8
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,780
    Post Likes
    Thread Starter
    joe,
    I'm thinking (hoping) it's not low on gas. 1.5 years ago, the charge was removed, pressure tested, pulled down to 500 microns and re-charged (850#) to dataplate amount.
    I will do a leak check to make sure.
    I've found the cartridge style reliefs leaking on several of the Trane screws by removing the relief discharge piping and putting a baloon over the relief outlet. Run the head up or leave the baloon on for a while and Wa La...Leak found!




    Originally posted by chiller joe
    think about your approaches 2 on cond 6 cooler you sound like you could be low on charge I had from fact low on charge and as your load changes oil return could be a problem also raise water to 44or 45

  9. #9
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,205
    Post Likes
    Jogas,
    I am having identical issues with two identical machines side by side. Seems to be when fully loaded. Was this the same in your case? Did you have the issue again?


    r404a

  10. #10
    Join Date
    Aug 2006
    Location
    jacksonville
    Posts
    87
    Post Likes
    Check your flow (pressure drop) thru the evaporator. Had a RTHD tripping on Low Oil Flow recently because of that.

  11. #11
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,205
    Post Likes
    Wisecrack,
    I had the controls tech at this job adjust his DPs to cut the machines out before they got to minimum flow. I am still leaning that way, but the issues always seem to come up at 100 percent load. Thanks for the reply.

    r404a

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •