  1. #40
    Join Date
    Feb 2003
    Location
    South Carolina
    Posts
    1,333
    Post Likes
    do you have a epa lic

  2. #41
    Join Date
    Jul 2005
    Posts
    28
    Post Likes
    Yes I do

  3. #42
    Join Date
    Jun 2005
    Posts
    59
    Post Likes
    If not on nameplate,then look under the out side cover for charging chart.

  4. #43
    Join Date
    Feb 2003
    Location
    South Carolina
    Posts
    1,333
    Post Likes
    then why cant you do this if you can pass that test
    you have to know how to charge a unit man

  5. #44
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Originally posted by pliscon
    Yeah Ok Prod... Me too. The subcooling value is not on the nameplate either..
    First, are you stating you are a regular homeowner and not a tech?

    Second, the SC will never be on the equipment data plate!

  6. #45
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Originally posted by prodiyer
    I dont use anything. Im just a homeowner that is learning from this site. I belieave the units will give you the required subcooling on the nameplate. Good Luck
    Then why did you state this "Ive got it covered !" in a earlier post?!?!

    And why, are you trying to help when there are 'true professionals' on this thread trying to help this guy?


  7. #46
    Join Date
    Jul 2005
    Posts
    28
    Post Likes
    Hey duc read my post.. I know how to charge it I am trying to clarify why it is if you charge the system according to the manual.... Eh.. Read the post I have written it about 8 times. I have only used super heat to charge or adjust Freon.. Based on the OEM Chart for Heil or ICP equip.. this is the only chart I have found. I got this from a school put on by a local supplier. This chart is better than the dinky chart in the installation manual. it is more specific. We have been installing mainly Luxaire or York Equip, with some Heil, Bryant, and a couple goodman. If you read my post I am trying to clarify that I am charging the system correctly because if you follow what it says in manual which I have been told by techs for the manufacturer, and techs at various supply houses where I have bought equip is the way to do it, the system is overcharged most every time. I am trying to determine whether the manual way of doing it is wrong or mabye I am doing something wrong. I Post here for some clarification. If I knew everything I probably would not be asking questions.

  8. #47
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Originally posted by pliscon
    Jult

    My ST is 44
    EST is 64
    IF this is actually correct, you have two figures that tell you everything you need to know about the systems charge!!!

    That's a 20 degree drop in the suction line from the coil to the condenser!!!

    This should tell you something! Now that it's pointed out to you, do you see something here?

  9. #48
    Join Date
    Jul 2005
    Posts
    28
    Post Likes
    Hey jult I was being sarcastic to his stupid homeowner post I am a Tech and am looking for some help.. I appreciate all the help you are giving me. Seems Prod is just being a prick though.

  10. #49
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Originally posted by prodiyer
    Stop adding for your lineset. What I was getting at is you cant trust the manufacturers charge. So you may or may not need to add for the lineset and evap. Pull your vacuum crack her loose and charge by superheat or subcooling.
    Read the last sentence in the paragraph above, THEN FOLLOW IT!!!

  11. #50
    Join Date
    Jul 2005
    Posts
    28
    Post Likes
    How can that suction line lose that much temp between the evap and cond Shouldnt it be gaining temp?

  12. #51
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Bingo!!!

    Now what would be the cause?
    I'll let you think a little so you will likely remember it for next time.

  13. #52
    Join Date
    Jul 2005
    Posts
    28
    Post Likes
    Wait a minute I went back down to my airhandler Now it is 45 leaving the coil mabye I didnt wait long enough after taping my probe on. Let me check outside..