    I had a new system installed consisting on the large Unico air handler in the attic (the home has hot water heat and hence no duct work) and a Trane 14i 5 ton compressor. The installers are known for being one of the best in our area. The installation crew (4 guys) did all the work in 4 days!

    Today was a hot one (90 degrees) and I couldn't seem to get the house under 78 degrees all day. I used a infared thermometer in the attic and it was 130 degrees up there. When I checked the air coming out of the tube-holes (not sure what they call them - little round 4 inch holes in ceiling) in the ceiling, it was 78 dgrees.

    Shouldn't the air temperature be colder than that? I checked the air conditioning in my car and it was 60 degrees.

    I live in Ohio along the lake and was wondering if my experience today is normal.

    I thought I bought the best unit available based on my issues.

    Any adice or comments welcome. Thanks in advance. Bugs

  2. #2
    Join Date
    Mar 2005
    Location
    Suppy NC
    Posts
    4,513
    sounds like you need to call the contractor and have them check it out. just what is wrong or to guess would not be fair to them.

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,330
    First the moderators aren't going to like the subject title and may delete the thread, this is a no price forum.

    Was the outdoor unit running.
    How many outlets do you have, the 4" things.
    Should have atleast 30 for your 5 ton unit.
    How long has the system been in.
    If its under warranty have you called them yet.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Senior Tech Guest
    Need a lot more info but my first advice would be call them and have them check it...78F is to warm...

  5. #5
    Join Date
    Aug 2003
    Posts
    6
    Sorry for the price issue.

    Yes the compressor has been running all day.

    There are exactly 30 of the duct ports.

    The system has been installed as of last summer/fall. It has a 10 year warranty but I wanted to get some input before I called them so I would understand their response as well as to make sure I was getting the right response.

    Thanks,

    bugs

  6. #6
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,330
    Give them the same info you gave us, and they should be able to take it from there.

    Too mnay possiblities for us to gave you things to ask.

    One question, have you changed, or cleaned your air filter lately.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Aug 2003
    Posts
    6
    Thanks for the input. As far as the filter, it's one of the electronic filters that I just cleaned about a month ago.

    I went up into the attic a few moments ago and noticed a white frost ice around the tube that goes into the coil area. Is that normal after running all day?


    Is it safe to say that the 78 degree is not normal coming out of the outlets? What would be the normal temperature coming out of the outlets?

    Thanks for any advice.

    Bugs

  8. #8
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,330
    The white frost is not normal for your indoor temp. And if they hooked up the freeze stat, your outdoor unit is shutting down periodically to protect it, and prevent the coil from becoming a solid block of ice.




    Usually between 25 and 30° cooler then return temp.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,754
    should not see ice anywhere. shut off compressor and just run indoor blower. call for service, let them know what you saw and did.

  10. #10
    Join Date
    May 2003
    Location
    Sarasota. Fl
    Posts
    1,286
    Originally posted by bugs
    Thanks for the input. As far as the filter, it's one of the electronic filters that I just cleaned about a month ago.

    I went up into the attic a few moments ago and noticed a white frost ice around the tube that goes into the coil area. Is that normal after running all day?


    Is it safe to say that the 78 degree is not normal coming out of the outlets? What would be the normal temperature coming out of the outlets?

    Thanks for any advice.

    Bugs
    Its "freezing up"....

    You have bad airflow or leaking refrigerant.

    Call your contractor ASAP..

    And turn the system off now ........
    It is the job of thinking people not to be on the side of the executioners.

    ~Albert Camus

  11. #11
    And throw that damn 'electrostatic' filter in the TRASH!

  12. #12
    Join Date
    Aug 2003
    Posts
    6
    Maybe I used the wrong term. The filter is a Honeywell Electronic Air Cleaner (F52F). It was pretty expensive.

    What should I have used in place of it?

    Thanks for any input,

    Bugs

  13. #13
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,316
    While I'm not a fan of electronic air cleaners, if kept washed, they are not restrictive of airflow.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event