    I have a package heat pump that is not cooling in the cooling cycle. I have a low amp draw, like 9.3 amps. I think my rating is 23.0 amps, and my gauge pressure is 150# suction, and #150 head while the system is running. It is a TXV system, with no reciever or accumulator. The suction and head seem to be equalized with the system running. The compressor cuts out on internal O/L before it shuts off. Could it be an issue of overcharge? or could it be a compressor with weak valves? I suspect the compressor has weak valves. Has anybody else seen this sort of thing?

    __________________________________________________ ________

    Thou shall install thermostat covers in public buildings!

    [Edited by phxhvac on 07-04-2005 at 11:31 PM]

  2. #2
    Join Date
    May 2004
    Location
    Canada
    Posts
    317
    Post Likes
    Your reading the same line my friendWhere are you taking your readings.....?

  3. #3
    Join Date
    May 2005
    Posts
    28
    Post Likes
    if your gage set is hooked up right and it is hot outside to give you 150 readings. itsounds like the compresor is gone
    low load amp draw
    over heating no freon flow to cool down unit
    age?
    condition?

  4. #4
    Join Date
    Sep 2001
    Location
    Vancouver Canada
    Posts
    996
    Post Likes
    Are you taking your readings at the commone suction port? 150 psi sounds like a lot of suction pressure. Also post your line temps, pressure won't tell you what is going on.
    "Go big or Go Home"

  5. #5
    Join Date
    Jul 2005
    Location
    Phoenix, AZ
    Posts
    266
    Post Likes
    Thread Starter

    Exclamation

    I traced the lines back to the reversing valve, the two ports on the outside of the Trane unit. The top one is connected to the middle of the three on the bottom side of the reversing valve(low side)(common suction). The bottom port is connected to the single line on the top of the reversing valve (High Side)(compressor discharge) It is a Trane rooftop package unit heat pump. The Trane unit is either 8 or 9 years old. I wanted to disconnect the condenser fan motor and let the head pressure rise to 475#, then cut out the unit without switching the reversing valve, to see if I have a hot suction line at the compressor or reversing valve line leaking by. But if I had an overcharge, wouldn't the amp draw go higher than the nameplate rating??? This unit is located in a clubhouse of an apartment building.

    __________________________________________________ ________

    Thou shall install thermostat covers in public buildings!

    [Edited by phxhvac on 07-04-2005 at 11:32 PM]

  6. #6
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    Sounds like a bum compressor, valves or broken shaft.

  7. #7
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,840
    Post Likes
    sounds like broken compressor

  8. #8
    Join Date
    Mar 2002
    Location
    Concord, CA
    Posts
    2,707
    Post Likes
    Your statements imply that it may be heating OK. Are the pressure readings normal in the heat cycle? If so then you probably have a reversing valve that's sticking.

  9. #9
    Join Date
    Jul 2005
    Location
    Phoenix, AZ
    Posts
    266
    Post Likes
    Thread Starter

    Exclamation Heating Cycle

    Didn't try heating cycle it is over 110 degrees here in Phoenix!

  10. #10
    Join Date
    Mar 2002
    Location
    Concord, CA
    Posts
    2,707
    Post Likes
    Pfft. And your point?

    You could try it for a few seconds just to see if the reversing valve is willing to move. Though if the readings are truly identical on both sides then it is probably a blown compressor. Even a stuck reversing valve isn't likely to completely equalize things.

  11. #11
    Join Date
    Jul 2005
    Posts
    88
    Post Likes
    Never seen suction pressure that high. My gauge only goes to 120 psi. I have had psi at 110 due to extreme indoor temp and unit cooling fine but no equal pressures. Sounds like that compressor is what I call "freewheeling". (broken crank?)

  12. #12
    Join Date
    May 2005
    Posts
    64
    Post Likes
    with both pressures being the same id say its dead compressor where do i get suction gauge that reads 150psi

  13. #13
    Join Date
    May 2005
    Posts
    28
    Post Likes
    if itas a roof top unit in 110 heat the sitting psi will be 150 easy

    anyone ever herd if a psi temp chart freon only needs to be about 85 to give a psi of 150

Page 1 of 2 12 LastLast