07-01-2005, 09:27 PM #1
Regular Guest
- Join Date
- Jul 2004
- Location
- Indiana
- Posts
- 27
WORKING ON A OLD CARRIER WITH A NO COOLING CALL,AS IM TAKING CAPS OFF SCRADERS OIL LADDEN REFRIGERANT COMES OUT THE BOTH VALVES . The pressure high went between 250 & 300 and the low showed none. The shell was cold and discharge line hot. The compressor was drawing 10 plus amps. Im thinking the suction valve is bad.
-
07-01-2005, 09:50 PM #2
Professional Member
- Join Date
- Jun 2005
- Location
- New York
- Posts
- 207
Why would you say the compressor is bad? You need to fix the pin or your hose so you can get a suction pressure reading. If there was an actual reading of 0psi, you wouldnt have a cold shell and it would most likly have been dead or off on internal when you got there. The compressor sounds good so far. Need just a bit more info on this machine and some operating info.. Was it running when you got there or you pushed the contactor in? Are you a service tech or H.O?
-
07-02-2005, 08:50 AM #3
Regular Guest
- Join Date
- Jul 2004
- Location
- Indiana
- Posts
- 27
Im A service tech at a apt complex Im recovering it today and pulling a vacccumm on it inside coil probabaly dirty also. Squirell cage fan was ok. Ultratech appreciate the input