    I've got a Lennox AHU I'm trying to figure out the capacity of. It's CBH19-41-1P looks like a 3.5 ton with 10 KW strip.
    Any help would be appreciated.
    Sean Cantrell
    3 ton
    Nov 2001
    east kansas
    You need to be very careful when sizing a AH with a Lennox heatpump. You must check the Engineering Data for correct matches.
    Dec 2003
    Corpus Christi TX
    airworx is correct
    41=3 ton
    46=3.5 ton
    Big leaps get you there faster, small steps keep you there longer.
    Nov 2001
    east kansas
    Gee Lynn, that was good advice. I would not sell a Lennox heat pump and AH without checking the Eng. Data first. I've seen the same AH matched with different size Outdoor units. Check it or be sorry come winter and you are locking out on high head pressure.