    New to the form. Homeowner question.
    I had a ac tech install a york heat pump and he didn't use any flux when he brazed the connection. Is this normal practice?
    Thanks txg

  2. #2
    Join Date
    Dec 2003
    Location
    Location!, Location!
    Posts
    929
    Yes, it can be normal with brazing alloys. There are some eutectic rods that have the flux on them already, and 45% needs flux, but most-dynaflow, 15- only need cleaning and, optimally, a nitrogen sweep during brazing. Soft solders require paste or acid(except in refrigeration systems) fluxes, but that's soldering, not brazing.

  3. #3
    Join Date
    Jul 2005
    Posts
    6
    Thank's for the reply.