    Whats the indoor wet bulb?

    Whats the outdoor ambient?

    What the coil delta?

    What is the complaint, not cooling at all, or just at higher outdoor temps?

    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    Join Date
    Apr 2003
    Posts
    81
    Originally posted by beenthere
    Whats the indoor wet bulb?

    Whats the outdoor ambient?

    What the coil delta?

    What is the complaint, not cooling at all, or just at higher outdoor temps?

    indoor wet bulb not taken because txv metering device, od ambient 85-90, I took coil delta but i'm not sure what it was at this time, complaint is unit not shutting off

  3. #16
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,595
    With a txv, if you take your indoor wetbulb, you know what your keaving drybulb temp should be.

    Does it get to set point but continue to run, or is the temp not coming down?
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #17
    Join Date
    Apr 2003
    Posts
    81
    [QUOTE]Originally posted by beenthere
    [B]With a txv, if you take your indoor wetbulb, you know what your keaving drybulb temp should be.

    Does it get to set point but continue to run, or is the temp not coming down? [/B
    braburn t-stat 5000, last night temp was 75 t-stat read 75 unit still running. lowered temp to 71 and let run for 24 hours unit got to 72 degrees, raised temp to 74 degrees and unit shut off, i don't think tstat is the problem, again why is subcooling relatively low and superheat low, I still feel that TXV is opening too much, please help.......lol

  5. #18
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,595
    For a 14 seer thats not a low subcool.

    It is a low super heat.

    Is this a swap out, or a new install.

    If a swap out, is it the same size as the old unit.

    If new was a load calc done.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #19
    Join Date
    Jun 2001
    Posts
    3,909
    Originally posted by mrbillpro
    No!
    Wouldn't the air traveling around the bulb cause some differance in the sensing? Or would it be negligable?

  7. #20
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,856
    Metal is a good conductor of heat, air not so good. The effect of the air would not be noticeable. I never insulate the bulb on walk-in's, and they work fine.
    Karst means cave. So, I search for caves.

  8. #21
    Join Date
    Jun 2001
    Posts
    3,909
    Originally posted by karsthuntr
    Metal is a good conductor of heat, air not so good. The effect of the air would not be noticeable. I never insulate the bulb on walk-in's, and they work fine.
    Thanks. It makes me wonder why Rheems come insulated and they are enclosed.

  9. #22
    Join Date
    Apr 2005
    Location
    San Luis Obispo County, CA
    Posts
    215
    The simplest answer is that insulating the bulb will not hurt anything. It will just ensure that the bulb is sensing the temp of the discharge line of the evap, like it is designed to do.

    So if you are looking at it, and questioning whether or not it will make a difference in the unit's operation, slap some wrap on that sucker and see what happens...

  10. #23
    Join Date
    Apr 2005
    Location
    Kingston Ontario Canada
    Posts
    1,210
    Originally posted by joe2003
    Does a TXV bulb need to be insulated if it is inside the plenum on the outlet of the evaporator?? I have a new replacement that has low cooling and the unit runs all the time. I spoke of this unit in a post earlier today but didn,t get but 1 reply...lol. If I add r22 to system or take it out my suction pressure stays at 75 pounds. Could the problem be that the bulb is not insulated, it came from the factory like that, should it be insulated?? This is a Tempstar coil.
    On my Carrier FV4A fan coil it says the TXV sensing bulb must be insulated on slope coils in horizontal right and downflow applications. Failure to insulate bulb will result in performance loss. Hope this helps

    Thorton

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event