    Not a real problem, "I HOPE!" but last night I replaced the contactor on the condensing unit for my neighbor. (Tempstar 3.5 ton, circa 1999) the compressor cycled, but the fan would not shut down on the CU.

    After I finished and had their system up and running again, I was have a beer or 12 with my neighbor at my home when I made comment that I had not had troubles with my CU (exact same one as his). about that time we walked into the house (needed more beer) and I noticed that it was 77 degrees on the t-stat, blower was working, went outside and CU was not running.

    Tripped breaker, damn and I was bragging on this Tempstar P.O.S. Reset breaker and started system, pulled cover off disconnect and check amp draw. 18.6 on both legs, Panel gives FLA of 18.7, so all is good.

    Just makes me wonder if I need to quit bragging on the quality or non-quality of equipment.

    Although I iwll be glad when this one dies so I will have an excuse to put a Carrier or Trane system in.

    Regards


  2. #2
    Join Date
    Feb 2005
    Posts
    344
    Post Likes

    What are you thinking???

    From the pan into the fire...

    Heh-Heh

    Have a beer on me.

  3. #3
    Join Date
    Feb 2003
    Location
    S.W. PA
    Posts
    3,298
    Post Likes
    should have knocked on wood

  4. #4
    Join Date
    May 2005
    Location
    Mississippi
    Posts
    102
    Post Likes
    Thread Starter
    Still curious as to why that darn breaker tripped though,

    Hoping was a thermal trip. heat Index was over 100 yesterday here and is expected to be 109 degrees heat index today.

    I wish someone would tell the damn weatherman that its not August in Mississippi yet.


  5. #5
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Originally posted by biscuitnt
    Not a real problem, "I HOPE!" but last night I replaced the contactor on the condensing unit for my neighbor. (Tempstar 3.5 ton, circa 1999) the compressor cycled, but the fan would not shut down on the CU.
    Please tell me how this is happening!

  6. #6
    Join Date
    May 2005
    Location
    Mississippi
    Posts
    102
    Post Likes
    Thread Starter
    Hmmmmm I give up... why?

  7. #7
    Join Date
    Oct 2004
    Posts
    875
    Post Likes
    Bet I know...

  8. #8
    Join Date
    Jun 2001
    Location
    Tx
    Posts
    3,917
    Post Likes
    Originally posted by control_noob
    Bet I know...
    Check to see where you put the common wire at. Just a hint.

  9. #9
    Join Date
    Nov 2001
    Posts
    1,874
    Post Likes
    Is it just me ?

    But almost 19 amps sounds high for running amps.
    Must be under a good load.
    If you try to fail, and succeed.
    Which have you done ?



  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Well, more then once while rushing, i've put the fan wire on the line side of the contactor, thinking i was putting the cch wire on.

    Always curse myself out when i do it .

  11. #11
    Join Date
    Nov 2001
    Posts
    1,874
    Post Likes
    usaully if you multiply the running amps by 5 or 6 .
    that would give a close expectation of the start amps

    18x5=90
    19x6=114

    maybe your breaker is getting weak.
    If you try to fail, and succeed.
    Which have you done ?



  12. #12
    Join Date
    Apr 2005
    Location
    San Luis Obispo County, CA
    Posts
    215
    Post Likes
    Originally posted by biscuitnt

    Just makes me wonder if I need to quit bragging on the quality or non-quality of equipment.

    Although I iwll be glad when this one dies so I will have an excuse to put a Carrier or Trane system in.

    Regards

    Actually, don't you know that all mechanical equipment talks to each other? You put new parts in your neighbors unit, now yours wants some too. Sort of like replacing the condensor fan motor only to have the compressor fail a week later...

  13. #13
    Join Date
    May 2005
    Location
    Mississippi
    Posts
    102
    Post Likes
    Thread Starter
    Originally posted by bb
    Originally posted by control_noob
    Bet I know...
    Check to see where you put the common wire at. Just a hint.
    I replaced the contactor on my neighbors unit, its perfectly fine.

    It was my unit that tripped the breaker when I was braggin on it never giving any trouble.

    Regards

  14. #14
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Toolpusher

    Multiply by 6.5 to 7 and that gives you L R A

    Starting amps can be in the hundreds for the first millisecond!

  15. #15
    Join Date
    Sep 2004
    Posts
    3,157
    Post Likes
    No , you all failed to see the real reason he had problems with his unit:

    I was have a beer or 12 with my neighbor at my home



    now multiply the LRA x the 12 beers and your answer will be the square of the headache after the beer

  16. #16
    Join Date
    Nov 2001
    Posts
    1,874
    Post Likes

    Starting amps can be in the hundreds for the first millisecond!
    [/B][/QUOTE]

    I've metered the start before and seen as much as 80 to 90.
    My meter has peak lock, so what ever the highest reading is it locks at that number.

    I've never seen one in the hunderds, on res. maybe comm.
    50 to 60 may be more commen in res.

    But I'm not desputing your claim.

    But how can lock rotor be lower the start amps,
    Lock rotor is full amps with no motor turn.
    Start amps are brief and then falls back.

    Make me understand.

    [Edited by Toolpusher on 07-01-2005 at 06:51 PM]
    If you try to fail, and succeed.
    Which have you done ?



  17. #17
    Join Date
    May 2005
    Location
    Mississippi
    Posts
    102
    Post Likes
    Thread Starter
    Have a beer or 12 like I do and everything makes sense!

    Regards and have a great day,

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •