Not a real problem, "I HOPE!" but last night I replaced the contactor on the condensing unit for my neighbor. (Tempstar 3.5 ton, circa 1999) the compressor cycled, but the fan would not shut down on the CU.
After I finished and had their system up and running again, I was have a beer or 12 with my neighbor at my home when I made comment that I had not had troubles with my CU (exact same one as his). about that time we walked into the house (needed more beer) and I noticed that it was 77 degrees on the t-stat, blower was working, went outside and CU was not running.
Tripped breaker, damn and I was bragging on this Tempstar P.O.S. Reset breaker and started system, pulled cover off disconnect and check amp draw. 18.6 on both legs, Panel gives FLA of 18.7, so all is good.
Just makes me wonder if I need to quit bragging on the quality or non-quality of equipment.
Although I iwll be glad when this one dies so I will have an excuse to put a Carrier or Trane system in.
Regards
-
What are you thinking???
From the pan into the fire...
Heh-Heh
Have a beer on me.
-
should have knocked on wood
-
Still curious as to why that darn breaker tripped though,
Hoping was a thermal trip. heat Index was over 100 yesterday here and is expected to be 109 degrees heat index today.
I wish someone would tell the damn weatherman that its not August in Mississippi yet.
-
Originally posted by biscuitnt
Not a real problem, "I HOPE!" but last night I replaced the contactor on the condensing unit for my neighbor. (Tempstar 3.5 ton, circa 1999) the compressor cycled, but the fan would not shut down on the CU.
Please tell me how this is happening! 
-
-
-
Originally posted by control_noob
Bet I know...
Check to see where you put the common wire at. Just a hint.
-
Is it just me ?
But almost 19 amps sounds high for running amps.
Must be under a good load.
If you try to fail, and succeed.
Which have you done ?
-
Well, more then once while rushing, i've put the fan wire on the line side of the contactor, thinking i was putting the cch wire on.
Always curse myself out when i do it .
-
usaully if you multiply the running amps by 5 or 6 .
that would give a close expectation of the start amps
18x5=90
19x6=114
maybe your breaker is getting weak.
If you try to fail, and succeed.
Which have you done ?
-
Originally posted by biscuitnt
Just makes me wonder if I need to quit bragging on the quality or non-quality of equipment.
Although I iwll be glad when this one dies so I will have an excuse to put a Carrier or Trane system in.
Regards
Actually, don't you know that all mechanical equipment talks to each other? You put new parts in your neighbors unit, now yours wants some too. Sort of like replacing the condensor fan motor only to have the compressor fail a week later...
-
Originally posted by bb
Originally posted by control_noob
Bet I know...
Check to see where you put the common wire at. Just a hint.
I replaced the contactor on my neighbors unit, its perfectly fine.
It was my unit that tripped the breaker when I was braggin on it never giving any trouble.
Regards