07-01-2005, 02:17 AM #14
You should be reading 8 to 12 ohms across a 24V contactor coil, you're definately shorted if you're only getting 1.
## + years in the field never made you a know-it-all
This industry is far more diverse than you are
-
07-01-2005, 08:25 AM #15
Regular Guest
- Join Date
- Jun 2005
- Posts
- 5
Re: did it
Yes, actually. The unit is for the daylight basement, and as such, used infrequently (never gets too hot down there). We went to run it for a while to give it some exercise and noticed it wouldn't come on. That's when we discovered the blown 3A fuse.Originally posted by Hroper
Blow the fuse before you replaced the T-stat?
From there it was trial and error, and today I think I'll order the replacement contactor from McMaster-Carr based on the help I've received here.
EDIT: I got the replacement contactor today and installed it. A/C runs like a champ, thanks to all who helped out.