  1. #14
    Join Date
    Feb 2005
    Location
    In a van by the river
    Posts
    621
    You should be reading 8 to 12 ohms across a 24V contactor coil, you're definately shorted if you're only getting 1.
    ## + years in the field never made you a know-it-all This industry is far more diverse than you are

  2. #15
    Join Date
    Jun 2005
    Posts
    5

    Re: did it

    Originally posted by Hroper
    Blow the fuse before you replaced the T-stat?
    Yes, actually. The unit is for the daylight basement, and as such, used infrequently (never gets too hot down there). We went to run it for a while to give it some exercise and noticed it wouldn't come on. That's when we discovered the blown 3A fuse.

    From there it was trial and error, and today I think I'll order the replacement contactor from McMaster-Carr based on the help I've received here.


    EDIT: I got the replacement contactor today and installed it. A/C runs like a champ, thanks to all who helped out.

    [Edited by strawewe on 07-01-2005 at 07:28 PM]