  1. #1
    My outside condenser is running as normal, as directed by the thermostat setting. The fan control is set to automatic. Problem is when the thermostat reaches its low temp it shuts off the condenser but does not shut off the fan which will keep running as if it was set to on.

  2. #2
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    14,897
    How old is the furnace or air handler?
    “I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay

    The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.

    No Guns…No Freedom…Know Guns…Know Freedom.










  3. #3
    The furnace and condenser were installed in 1990. Thanks for your help.

  4. #4
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    14,897
    0 that's close to the change over to boards so it could be a bad relay on the board or a bad fan relay, we are talking the inside fan continues to run right?
    “I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay

    The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.

    No Guns…No Freedom…Know Guns…Know Freedom.










  5. #5
    Yes, it is the furnace fan that continues to run.

  6. #6
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    14,897
    Need furnace Brand & Mod# to have a clue.
    “I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay

    The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.

    No Guns…No Freedom…Know Guns…Know Freedom.










  7. #7
    Join Date
    Aug 2004
    Location
    Kentucky & Michigan
    Posts
    313

    Red face

    newer furnace, bad IFC would be the most likely. Old furnace fan control circuit problem..probably IFR. Running continuously is not a hazard..but if it's a newer furnace, I'd have a Tech check it before winter...the IFC controls a lot more than the fan.
    "Surprised ?! If I woke up tomorrow with my head sewn to the carpet, I wouldn't be more surprised."
    Clark Griswold

  8. #8
    It is an Amana Air Command Hi Eff 90 Gas.

  9. #9
    Join Date
    Aug 2004
    Location
    Kentucky & Michigan
    Posts
    313
    barring extemporaneous circumstances.. it sounds like a bad IFC. Is there an error code ? The ifc controls combustion air, ignitor timing, gas valve timing, and all safeties. Get it checked before winter.
    "Surprised ?! If I woke up tomorrow with my head sewn to the carpet, I wouldn't be more surprised."
    Clark Griswold