Results 1 to 7 of 7
Thread: cfm per btu
    NE OHIO
    cfm per btu
    how much cfm do you need for 70000btu furnace, new install with 2 10inch round returns same supply
    I don't know
    NE OHIO
    HUH
    Depends on its efficiency and the allowable temp rise.
    For a 55°F temp rise. At 80% eff, 940CFM, at 90% eff, 1060 CFM, and for 95% eff, 1120 CFM. Whcih your 2 10" aren't good for any of the above CFMs.
    NE OHIO
    its a 95 didn't think it was enough, our wonderful installers Thanks beenthere
    Mar 2011
    Northeast Missouri
    The formula I have used for a condensing furnace is to divide the input BTU by 10,000 and then multiply that number by 150(cfm for a condensing furnace) So roughly 1050 cfm, your return is a little short. I would watch that heat rise cause I bet your on the high end of it or even over. And as a side note I have been down that road with our installers too, just remember keep it professional.
    Rochester NY
    Here's a great example of expectations and reasonableness being totally disconnected. Homeowners buy replacement furnace (maybe not in this case, but I'll use this as a common example) and expect the hvac company to know everything about issues with the house, the duct work, etc, all based upon the "free estimate".
    Your free estimate got you little to no engineering. By getting 6 free estimates you put a lot of cost on 6 hvac companies, which really means YOU pay for that in your price.
    We understand the consumer thinks this is how to get a furnace as "cost effectively" as possible, but once you signed that free estimate, unless your bid specification included a lot of diagnostics and design, you got the furnace quoted installed as quickly as possible.
    Did you have a specification?