    Glycol leaked into Liebert A/C system

    Found a Liebert Mini Mate (1.5 ton) that was tripped out. Self contained unit with glycol cooled condenser. When testing system pressures got a lot of oil coming out of the hoses, then found glycol coming out too. Turns out the scroll compressor is filled with glycol. Found the 3-way valve for the glycol cooled condenser had a leaking belows. When blowing some nitrogen through the evaporator and condenser I can hear gurgling sounds.
    Planning on replacing the compressor, txv, filter drier (plus add a suction filter). Has anyone experienced this problem before and if so what are the chances of cleaning up the evaporator and condenser using a flush kit? Any other suggestions to clean it up??
    Thanks

  2. #2
    Join Date
    Jun 2008
    Location
    NY
    Posts
    33
    Post Likes
    I had a water cooled unit do the same thing and we were able to get it flushed. However I think with the glycol the whole unit should probably be replaced. In addition the the parts mentioned you need to replace the condenser coil also. Good Luck

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    The glycol portion of this equation is what bothers me.

    I KNOW that water can be removed from a system. Driers and evacuation along with blowing lines out with nitrogen will do that quite handily.

    What I DON'T know is what will happen to the glycol portion of the solution. Will that remain as a contaminant in the system? or will it be removed by the driers/evac/purging process?



  4. #4
    Join Date
    Apr 2006
    Posts
    337
    Post Likes
    I'll bet once glycol is in the system, it's there in some form forever. Just think about when you work with glycol how quickly your hands dry out. Think about what it does to pump seals. Think about what a pain it is to get a soldered joint repair to take that had glycol running through it. I'd replace the unit.

  5. #5
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,307
    Post Likes
    I cannot begin to imagine the end result of the glycol, ref., ref. oil and elevated temperatures is going to produce in the long run. I have seen some nasty mixes of a contaminated ref. system from clorine, Hydrocloric acid, chromic acid, sulpuric acid and even a phosgene condenser in Baton-Rouge @ the BASF plant where tank cars of phosgene were produced. But Glycol?? I hope whatever the outcome is on this one that the poster shares the end result with us...Might be very interesting.(Might even be explosive also)
    Ain't "None" of us as smart as "All" of us..

  6. #6
    Join Date
    Mar 2007
    Location
    Orange County NY
    Posts
    218
    Post Likes
    Quote Originally Posted by acrefrig View Post
    Found a Liebert Mini Mate (1.5 ton) that was tripped out. Self contained unit with glycol cooled condenser. When testing system pressures got a lot of oil coming out of the hoses, then found glycol coming out too. Turns out the scroll compressor is filled with glycol. Found the 3-way valve for the glycol cooled condenser had a leaking belows. When blowing some nitrogen through the evaporator and condenser I can hear gurgling sounds.
    Planning on replacing the compressor, txv, filter drier (plus add a suction filter). Has anyone experienced this problem before and if so what are the chances of cleaning up the evaporator and condenser using a flush kit? Any other suggestions to clean it up??
    Thanks
    Clean up as you are planning, with the flush, use a canister type suction filter replacing the core daily. Then plan on replacing the compressor a second time, the first replacement will clean up the system and then die unless your real lucky.

  7. #7
    Join Date
    Aug 2006
    Posts
    3,691
    Post Likes
    Replace the entire unit, it will never work right again. Also if it should fail and crash Servers or a small computer room the loss could be much greater than a replacement.

  8. #8
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    185
    Post Likes
    Well you wouldn't have to worry about moister in the system freezing at the TXV. Really though 1-1/2 ton unit? Replace it and be done with it.

  9. #9
    Join Date
    Feb 2010
    Location
    Ontario Canada
    Posts
    1,341
    Post Likes
    The cost of the work envolved to get this unit working properly, is much more that the replacement of the unit...

    Replace the unit and be done with it....

  10. #10
    Join Date
    Feb 2011
    Location
    colorado mountians
    Posts
    117
    Post Likes
    Agree, dont waste your time or customers money. By the time you do everything under the sun and have to go back repeatedly ( who's payin?) just replace the whole thing and be done with it. Too many times wanted to be a nice guy and try to save the customer some coin just to be bit in the a$$

  11. #11
    Join Date
    Nov 2001
    Location
    Seattle, WA
    Posts
    8,352
    Post Likes
    Had a dot.com customer hire me to start a factory rebuilt one. Went to check the pressures and they were low so I cracked my hose to smell the refrigerant and got a face full of glycol......will never make that mistake again.

    Contacted the factory and they said fix it. I said no and told the customer to make them give him another one pre-tested before it gets out of the factory this time.
    "The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
    - Alexis de Toqueville, 1835

  12. #12
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes

    give the option

    i would give the option to the customer., that you can do both., leave it up to them!
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  13. #13
    Join Date
    Sep 2010
    Posts
    5
    Post Likes
    Thread Starter

    Going to fix it

    Thanks for all the input on this problem. To update, I priced out a new compressor, evap, txv etc etc and we are going to rebuild the whole thing- anything that glycol got into basically. With labor it will be about half the cost of a new one.

  14. #14
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    185
    Post Likes
    Good luck to ya... Hope all goes well.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •