Thread: condensate drain trapping
-
06-28-2005, 01:32 PM #1
Regular Guest
- Join Date
- Jun 2005
- Posts
- 3
I've been perusing through the Residential and Wall of Pride forums and have a question about condensate trapping on condensing furnaces. If the condensate is draining from furnace through 3/4" piping and into a pump, would a drain trap still be necessary? This an upflow system, a-coil on top, and condesing furnace. I haven't seen alot of pictures in the wall of pride section showing drain traps on some 90% units and was wondering what people are doing.
-
06-28-2005, 02:25 PM #2
Professional Member
- Join Date
- Apr 2005
- Location
- NE PA
- Posts
- 697
You should have a trap in almost all instances.
Read: http://www.trane.com/commercial/issues/iaq/iaq5.asp
for the long story on traps.
paul
-
06-28-2005, 02:32 PM #3
Professional Member
- Join Date
- Jul 2004
- Location
- midwest
- Posts
- 2,868
There is a trap in all 90% furnaces already so I never trap them again.
-
06-28-2005, 02:44 PM #4
what trane said
-
06-28-2005, 03:01 PM #5
long answer made short you PROBALLY do not need a trap if you are using a 90+ and a condensate pump
however a trap would not hurt
-
06-28-2005, 03:04 PM #6
Regular Guest
- Join Date
- Feb 2004
- Posts
- 360
Thanks for the article. I'll be putting a trap on this weekend.
-
06-28-2005, 03:37 PM #7
Professional Member
- Join Date
- Jul 2004
- Location
- midwest
- Posts
- 2,868
Great, now all 90,s are going to be double trapped. It won't hurt but it also won't help. All you are doing is adding a likely place for the drain to cause future problems.
-
06-28-2005, 03:58 PM #8
Regular Guest
- Join Date
- Jun 2005
- Posts
- 3
I see. Thanks everyone for clarifying.
-
06-28-2005, 04:14 PM #9
Regular Guest
- Join Date
- Feb 2004
- Posts
- 360
I have an 80 and no trap between the humidifier and condensate drain. My drain is plumbed directly into the sewer and there is a trap there, but it has occoured to me that since there is an opening at the humidifier where air can be sucked in, and a place for it to go into the air handler through the drip tray, that I need another trap.Originally posted by trane
Great, now all 90,s are going to be double trapped. It won't hurt but it also won't help. All you are doing is adding a likely place for the drain to cause future problems.
-
06-28-2005, 06:19 PM #10
I've been told when using a condensate pump, no trap is needed. Therefore, I've never installed one when using a pump. If this is incorrect, please clarify so I can correct this.