Thread: A/C sizing

  1. #1
    Join Date
    Mar 2005
    Posts
    7
    Post Likes

    Confused

    From all I've been told, any house with less than 1600sq ft. would be unwise to use 2ton A/C as it will not properly remove humidity and result in a loss of the SEER value, due to constantly going on and off....any thoughts on this??

    Also, rough rule of thumb is given as 1Ton per 1000sq ft??

  2. #2
    Join Date
    Jul 2004
    Location
    midwest
    Posts
    2,869
    Post Likes
    Somebody is telling you wrong.

  3. #3
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes


    Guessing and/or using so called rules of thumb do not produce good results. Your need to read this.

    http://www.hvac-talk.com/vbb/showthr...threadid=33866


    A proper load calculation is the ONLY way to properly size a system!

  4. #4
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Originally posted by sd47
    Also, rough rule of thumb is given as 1Ton per 1000sq ft??
    I think that rule of thumb only applies in Alaska.

    I would love to see you cool a 5000 sq.ft. home in Houston, Tx. with a 5-ton a/c.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  5. #5
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes

    Thumbs down Thumb Sized

    Originally posted by sd47
    ... any thoughts on this??

    Also, rough rule of thumb is given as 1Ton per 1000sq ft??
    This can almost be applied to homes With One 2' x 4' Window + maybe 1 Door__ Along with the ALASKA igloos.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  6. #6
    Join Date
    Mar 2005
    Posts
    7
    Post Likes
    Thread Starter
    Apparent I missed the obvious factors like direction of house facing, window area, shade factor, ceiling height, and a lot more, but what I was driving at was more todo with the SEER reduction than anything else??...or maybe I just answered myself...

  7. #7
    Join Date
    Mar 2005
    Posts
    7
    Post Likes
    Thread Starter
    I do appreciate the sarcasm however, although it wasn't particularly conducive to wanting to open my mouth again...lol

  8. #8
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes

    Equpment Selection

    Originally posted by sd47
    Apparent I missed the obvious factors like direction of house facing, window area, shade factor, ceiling height, and a lot more, but what I was driving at was more todo with the SEER reduction than anything else??...or maybe I just answered myself...
    ...
    1600 Sq. Ft may be well served by
    a 2.5 or 3-ton, high SEER unit
    with Variable Speed Air Handler.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  9. #9
    Join Date
    Mar 2005
    Posts
    7
    Post Likes
    Thread Starter
    I see you're in SWFlorida..so I guess I should have stated that I am in SW Ontario, Canada, where we get temps like 87 with humidex of 94 during our "heat waves"...and normal would be more like 82 with humidex of 88...much the same variance, but easier to live with the second set of numbers, if nothing else...

  10. #10
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes

    Variations

    Originally posted by sd47
    I see you're in SWFlorida..so I guess I should have stated that I am in SW Ontario, Canada, where we get temps like 87 with humidex of 94 during our "heat waves
    So perhaps, Igloos design rule may be Applied.

    There might more than just a slight variation between the
    Artic ( Ontario) and the Tropics (S. FL)

    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  11. #11
    Join Date
    Mar 2005
    Posts
    7
    Post Likes
    Thread Starter

    Confused

    Assuming the Igloo rule is in effect,,what is the point behind using a 21/2Ton coil with a 2Ton unit??

  12. #12
    Join Date
    Aug 2003
    Posts
    626
    Post Likes
    Mrbillpro--If you look at some of the Building America homes by Pulte in Houston you will see about 1 ton per 1000 sq. ft. It's all in the way you build the home.

  13. #13
    Join Date
    Nov 2002
    Location
    VA
    Posts
    296
    Post Likes
    sd47

    "what is the point behind using a 21/2Ton coil with a 2Ton unit?"

    The same physical coil element is rated at different capacities depending on the refrigerant control device supplying it. What this means is actual coil is a complex factor depending on more variables than mentioned thus far in this thread...

    The only true authority on each unit is the vendor's rep that has to approve the replacement if there is a warranty claim (sad but true). Actually the engineers who design the Coils are totally aware of the performance curves from empirical testing data (which may differ from the original design data).

    HVAC professionals have to go by the numbers and matching units provided be each vendor. There are times when "field modifications" are approved but they are the exception, not the rule.

    What I’m attempting to say is do not focus on capacity numbers, but rather on compliance with the vendors specifications. Does this make sense?

  14. #14
    Join Date
    May 2002
    Location
    Colorado
    Posts
    697
    Post Likes
    Originally posted by uktra
    Mrbillpro--If you look at some of the Building America homes by Pulte in Houston you will see about 1 ton per 1000 sq. ft. It's all in the way you build the home.
    And design, install and commission the HVAC system.

  15. #15
    Join Date
    Aug 2003
    Posts
    626
    Post Likes
    Good job Panama--I should have included that!!

  16. #16
    Join Date
    Mar 2005
    Posts
    7
    Post Likes
    Thread Starter
    What I’m attempting to say is do not focus on capacity numbers, but rather on compliance with the vendors specifications. Does this make sense?

    Absolutely, so the next question is where do you go to find the vendors specs without having to ask anyone...just trying to filter out diff opinions of diff HVAC contractors, so as not to confuse opinion with fact...thanks

  17. #17
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes

    Question Learn from the ' Best '

    Originally posted by uktra
    Mrbillpro--If you look at some of the

    Building America homes by Pulte in Houston
    you will see
    about 1 ton per 1000 sq. ft.

    It's all in the way you build the home.
    UKTRA,

    Please provide link to specifics like Floor Plan,
    Window Area, S.H.G.C., U-value, Insulation values, ...

    Now that's something WE Can ALL Learn from:
    1,000 Sq. Ft./Ton

    Does anyone else in Houston build to that level?

    I'd like to know how to get just half way there...
    800 S.F./Ton
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  18. #18
    Join Date
    Aug 2003
    Posts
    626
    Post Likes
    Look up DOE's Building America site. Also [url]http://www.buildingscience .com

  19. #19
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes

    Thumbs up

    I appreciate it
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •