    Micro-Channel

    Have you had a bad experience yet?

  2. #2
    Join Date
    Jul 2009
    Location
    Michigan
    Posts
    103
    The serviceability of a leak and blockages with-in the refrigerant circuiting is what I am concerned with.

  3. #3
    Join Date
    Aug 2002
    Location
    Greenville SC
    Posts
    431
    I'm still waiting to see what happens to one after a bad burn out.

  4. #4
    Join Date
    Jul 2009
    Location
    Michigan
    Posts
    103
    I can tell you what happens after one bad install.

  5. #5
    Join Date
    Mar 2011
    Location
    East Coast FL
    Posts
    1,056
    I agree with most of you guys. Micro-channel is something else. Not what we can work on and repair , what we're used to. Ya , the charge is A LOT more critical , now we have large equipment that is to be charged like an ice machine. The old stuff was repairable and flexible. Seems like all the OEM's are into reducing the total operating charge lately....look at supermarket refrigeration for example....big time there... And that is what the micro-channel is all about. Temporary satisfy the gov. We are going to see some huge fundamental changes in this industry during the next 10-20 years and this new coil is just the introduction. Why are they not using it for the evaporator??? Or are they? It is bogus and ya after one burnout or system contamination you loose many parallel circuits?? How are you supposed to deal with that?? Replace the coil?? Suuuuuuure , lets sell more parts and hopefully people recycle. Micro-channel may be more efficient , dont know , not a labratory math major. But it's old school for this guy.

  6. #6
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,923
    Quote Originally Posted by awatson84 View Post
    yes i installed a guardian 2.5 ton 410a and over charged it by about 9 ounces lost a compressor in 24 hrs it was the first one i had put in amps where good superheat was there sub cooling was there had a txv thought i was fine let it run for about an hour why i was there come to find out u can over charge one by 6 ounces i do not like them i have put about 12 in now and i measure the line set and add to installation manual have yet to do the rtu micro channel r22 was not bad the 410a ridiculous
    So, you had a problem on a system that was overcharged and you are blaming the coil?
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  7. #7
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,923
    Quote Originally Posted by acwizard View Post
    There are a few mfg. that are using them in evaporators. The evaporator has a few more challenges than the condenser coil. Primarily the water run off from condensation and funneling it into the condensation pan. Blow by and proper airflow are more critical. This technology has been around for quite sometime especially in the automotive industry. They have been proven to be more efficient in heat transfer and do to the price of copper mfgs. have found a way to reduce costs and increase profits. They can be field repaired. I have only seen some problems with a makeup air unit and R-410 out in the desert. They all leaked, not enough airflow across coil, mfg replaced all coils with different design and problem disappeared. There is probably going to be a learning curve for everyone as more and more of these appear out in the real world.
    Could you please tell us what manufacturer's are using microchannel coils for evap coils?
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  8. #8
    Join Date
    Mar 2011
    Location
    East Coast FL
    Posts
    1,056
    So we cannot use pumpdown with micro channel without a receiver , which is not normally employed with a/c duty. You loose your subcooling with a receiver. That is why.

    acwizard , I respect your knowledge...care to enlighten us on how a leak repair is performed on the micro-channel coil??

    Why do you loose your subcooling with a receiver? Because anytime you have refrigerant in a vessel with vapor and liquid present , you are at or close to saturation. There may be a few degrees available at the bottom but not anything to speak of.

    Carrier is suggesting to abort pumpdown on larger commerical splits and instead go with a liquid line drop solenoid as well as liquid line check valves with R-410A. To prevent migration and flooded starts.

    When you look at micro-channel cross section , it is hard to imagine room for condensing or even hot gas flow through those tiny , tiny , passages.

    Durable and efficient it may be , cannot see it happening on a DX evaporator.

  9. #9
    Join Date
    Mar 2011
    Location
    East Coast FL
    Posts
    1,056

    No Evap

    They're not using micro-channel for the evaporator coil , b/c it needs expansion. Pressure drop , not pressure increase. Sorry , but there is no room or volume for refrigerant boiling with that design. Yes micro-channel has been around forever....in automotive. Reducing the temperature of a coolant. A fluid cooler. Quite a bit different than DX refrigeration. My motorcycle has one on its radiator. Seems to work fine. Lets leave em there.

  10. #10
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,923
    Their ability to shed condensate is also an issue.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  11. #11
    Join Date
    Mar 2011
    Location
    East Coast FL
    Posts
    1,056
    You guys are on it.

  12. #12
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,702
    Quote Originally Posted by dave sulz View Post
    i installed a 50 ton carrier split this winter. charged by weight. no way to pump down. this worries me. carrier says no chemicals to clean coil. dusty and planty dust will be a disaster clogger. in my opinion.
    Did you order the digital scroll too.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  13. #13
    Join Date
    Mar 2004
    Location
    midwest
    Posts
    954
    Just had a to repair a Larkin unit, not many if any vendors carry any repair kits. York parts had a solder type kit we used, it worked. Many I see are epoxy type. Problem is most newer systems have POE oil in them, so you blow a charge and its open for more than 12 hours you got problems.

    What do you do to clean up a hermetic scroll system besides a dryer change out?

    Any better ways to repair leaks?
    An astronaut stuck in space was asked by a reporter, "How do you feel?"
    "How would you feel," the astronaut replied, "if you were stuck here, on top of 20,000 parts each one supplied by the lowest bidder?"

    "do it right or do it twice"

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event